Reza, No I minute is OK. BUT be careful of over pressurization due to the high 
rate and high
concentration. The intent was to allow designers some latitude when using very 
high concentrations
thus minimizing pipe sizes and preventing over pressurization the room and 
popping windows and such.
See venting consideration and calcs in 5.6

Most computer rooms are protected under the "Dry electrical Hazard" as you have 
done. I believe that
you may take advantage of the extended discharge time if you wish or need to. 

Now the big question! Why CO2  when other clean agents are safer, cheaper and 
arguably the industry
standard?  


Burton Ford
SET, CFPS
Member AFAA
[EMAIL PROTECTED]
267-487-1000
Fax 267-487-1010

This e-mail transmission contains information that is intended to be 
confidential and privileged.  If
you receive this e-mail and you are not a named addressee you are hereby 
notified that you are not
authorized to read, print, retain, copy or disseminate this communication 
without the consent of the
sender and that doing so is prohibited and may be unlawful.  Please reply to 
the message immediately
by informing the sender that the message was misdirected.  After replying, 
please delete and otherwise
erase it and any attachments from your computer system.  Your assistance in 
correcting this error is
appreciated.  Thank you.  Cintas Corporation

 -----Original Message-----
From:   [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED]  On
Behalf Of Reza Esmaeili
Sent:   Thursday, August 23, 2007 10:19 AM
To:     [email protected]
Subject:        Carbon Dioxide System Discharge Time

Hi all,
  For designing a total flooding high pressure carbon dioxide system in a 3,500 
cubic feet computer
room with electrical equipment and cable runs, I have specified my room as "Dry 
electrical hazard"
with flooding factor of 0.083 lb/cubic.feet and 50% design concentration 
according to NFPA-12.
  My questions are as below:
  1)- Is a computer room fire a deep seated fire?
  2)- NFPA 12 states that "For deep-seated fires, the design concentration 
shall be achieved within 7
minutes, but the rate shall be not less than that required to develop a 
concentration of 30 percent in
2 minutes." Is it a problem if the total discharge time would be only 1 minute 
for this case?
  Many thanks for your help in advance.
  Reza

       
---------------------------------
Pinpoint customers who are looking for what you sell. 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.  Your assistance in correcting this 
error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to