CO2 is often preferred in the developing world because it is universally available - the installation cost may not actually be the defining factor as the cost and difficulty of gettting a recharge can outweigh other benefits. I saw an u/s chemical gas system in the Sudan a couple of months ago, it had ben like that for a year as there was a problem getting a recharge through customs. If life safety is an issue (ie if the space is regularly occupied) then agent of choice is either an inert but life safe gas like Inergen or a chemical gas like FM200 . Some jurisdictions and insurers do not favour FM200 . Don't forget there are pending amendments to NFPA 2001 which will affect things like overpressure flaps.

New agent Noveon looks tasty but has limited availability in many places and I have seen prices which look out of line with competing products.

But the real question is: What's wrong with sprinklers or mist ? I specify these all the time for IT and comms rooms.

Stewart

Stewart Kidd
Loss Prevention Consultancy
Cambridge, England


Reza, No I minute is OK. BUT be careful of over pressurization due to the high rate and high concentration. The intent was to allow designers some latitude when using very high concentrations thus minimizing pipe sizes and preventing over pressurization the room and popping windows and such.
See venting consideration and calcs in 5.6

Most computer rooms are protected under the "Dry electrical Hazard" as you have done. I believe that
you may take advantage of the extended discharge time if you wish or need to.

Now the big question! Why CO2 when other clean agents are safer, cheaper and arguably the industry standard?

Burton Ford
SET, CFPS
Member AFAA
[EMAIL PROTECTED]
267-487-1000
Fax 267-487-1010

This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is
appreciated.  Thank you.  Cintas Corporation

 -----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Reza Esmaeili
Sent:   Thursday, August 23, 2007 10:19 AM
To:     [email protected]
Subject:        Carbon Dioxide System Discharge Time

Hi all,
For designing a total flooding high pressure carbon dioxide system in a 3,500 cubic feet computer room with electrical equipment and cable runs, I have specified my room as "Dry electrical hazard" with flooding factor of 0.083 lb/cubic.feet and 50% design concentration according to NFPA-12.
  My questions are as below:
  1)- Is a computer room fire a deep seated fire?
2)- NFPA 12 states that "For deep-seated fires, the design concentration shall be achieved within 7 minutes, but the rate shall be not less than that required to develop a concentration of 30 percent in 2 minutes." Is it a problem if the total discharge time would be only 1 minute for this case?
  Many thanks for your help in advance.
  Reza

---------------------------------
Pinpoint customers who are looking for what you sell.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to