The occupancy is a nursing home outside of town with no municipal water
supply. This building is currently supplied by a water tower. We have come
to find out that the water tower is not heated and freezes in the winter
time (this is Nebraska), apparently the domestic demand from the tower
maintains about a 6" column of unfrozen water in the winter. While this
"column" of water is sufficient for domestic demand, we know it won't be for
the fire protection demand.
   

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, September 13, 2007 10:04 AM
To: [email protected]
Subject: RE: Fire Pump

What is the application,  commercial, industrial or residential? 


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David
Autry
Sent: Thursday, September 13, 2007 10:47 AM
To: [email protected]
Cc: Doug Hohbein
Subject: Fire Pump

Dear Forum,

NFPA 13 (2002) 15.2.2*
Pumps. A single automatically controlled fire pump installed in
accordance with NFPA 20, Standard for the Installation of Stationary
Pumps for Fire Protection, shall be an acceptable water supply source.

A15.2.2
An automatically controlled vertical turbine pump taking suction from a
reservoir, pond, river, or well complies with 15.2.2.

I have an owner that wants to supply domestic water and fire protection
water with a vertical turbine pump on a well.

Does this pump need to be installed per NFPA 20?
Does this pump need to be a listed fire pump?

I've always ASSUMED that if a pump supplied fire protection it needed to
be a listed fire pump installed per NFPA 20. Now I'm not so sure.


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to