I kind of thought that 8.6.5.2.2 applied to standard upright and pendant
sprinklers regardless of occupancy?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, September 14, 2007 11:40 AM
To: [email protected]
Subject: RE: Floor-mounted vertical obstruction

Bill,
The original question was for ordinary hazard areas such as storage lockers.
8.6.5.2.2 only applies to light hazard areas.  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Friday, September 14, 2007 11:00 AM
To: [email protected]
Subject: RE: Floor-mounted vertical obstruction

 I would have thought that 13-2002: 8.6.5.2.2 & table & figure would govern?
Or educate me?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Friday, September 14, 2007 10:33 AM
To: [email protected]
Subject: Re: Floor-mounted vertical obstruction

Similar to how we treat libraries where the 18 inch is violated by the
aisles.

Roland

On Sep 11, 2007, at 7:03 AM, Ed Kramer wrote:

> Dewayne, I don't think you can apply the 3-times rule to partial- 
> height walls.  The 'appendix' section A.8.6.5.2.1.3 explains it's 
> intended for obstructions where water can be thrown over & under (such

> as a horizontal pipe).  If you have partial-height walls with less 
> than 18" of clear space from deflector to top-of-wall, I think you'll 
> need to install sprinklers within each 'compartment' (as if the walls 
> extended up to the roof deck).
>
> Ed Kramer
> Littleton, CO
>
>
>> We just looked at something similar yesterday AM, and #13-2002
>> 8.6.6 was
>> pretty clear about just maintaining 18" clear below the deflector 
>> being adequate. The 3x rule started getting into the 6-deep cross- 
>> referenced rules where my eyes glazed over and we already had our 
>> answer. But you're half-way there!
>>
>> glc
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of 
>> Dewayne Martinez
>> Sent: Tuesday, September 11, 2007 7:19 AM
>> To: [email protected]
>> Subject: Floor-mounted vertical obstruction
>>
>> I am not sure if this got up to the list yesterday so I am sending it

>> again.
>> It is odd that there was no response, any input would be appreciated.
>>
>> ________________________________
>>
>> From: Dewayne Martinez
>> Sent: Monday, September 10, 2007 11:23 AM
>> To: '[email protected]'
>> Subject: Floor-mounted vertical obstruction
>>
>>
>> We are bidding a self storage building that will have partial height 
>> walls (5ft on center) to 2ft below the deck with chain link fence to 
>> the deck.  This will be designed to an OH II density so the rules for

>> floor-mounted vertical obstructions will not apply since they are for
>> light hazard only.   If we can arrange it so that the wall is more  
>> 18in
>> below the sprinkler deflector can we ignore them per 8.6.5.3 (13 
>> (o7ed))?  If the top of the wall is closer that 18in to the deflector

>> do we follow 3 times rule?  Thanks for your input in advance.
>> Dewayne Martinez, CET
>> Design Build Fire Protection
>> [EMAIL PROTECTED]
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [EMAIL PROTECTED] (Put the word unsubscribe in the subject
>> field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [EMAIL PROTECTED] (Put the word unsubscribe in the subject
>> field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject
> field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to