Just a word of caution regarding low differential DPV supervisory air or any 
critical low air alarm. Always use a calibrated test gauge to set the pressure 
switch. Trying to find 7 PSI on a the best gauge that $5.00 can buy will always 
be a challenge. At one time some of the valves came with gauges with 0-300 lb 
scales . . . a standard trim gauge. . .  in my view not suitable for the 
application. A good gauge with a scale of 0-50 lb would be a worthwhile 
investment when dealing with such low pressures. 

Mike Cabral

---- George Church <[EMAIL PROTECTED]> wrote: 
> What if its one of those new-fangled low differentials that runs on 13 PSI. 
> Won't the customer complain of the constant trouble signal? I know, reset
> it. 
> 
> However, if it sits at 13 PSI and trips at 7, where do the wiring guys get
> off telling us the proper drop in pressure and making it code? A low air
> that goes off 4 PSi below the trip point is of little value. Guess it makes
> a nice high air alarm, if that's what we were concerned with.
> 
> Guess that's why our buildings here in PA don't get any alarms, eh?
> 
> glc
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Charles
> Thurston
> Sent: Tuesday, October 23, 2007 6:04 PM
> To: Dave Phelan
> Subject: Re: Supervisory Alarm - Low Air
> 
> Hello Dave,
> 
> If the "little red box" is a Potter PS40-2A is has 2 sets of contacts
> in it. One for "Low Air" and the other for "High Air". It is factory
> set to operate on Increase at 50 PSI and on Decrease at 30 PSI. The
> set pressure can be adjusted from 10-175 PSI. The 2 switches can be
> adjusted  independently of each other to anywhere in that range.
> 
> If the "little red box" is a Potter PS40-1A it only has 1 set of
> contacts that operates on decrease. If is factory set to operate on
> decrease at 30 PSI.
> 
> I would think the newer System Sensor brand can do the about the same.
> 
> I have found that most of the time the alarm company does not tie into
> the high pressure switch.
> 
> 
> 
> 
> Tuesday, October 23, 2007, 5:52:35 PM, you wrote:
> 
> > Something new to me popped up today as we are now using the 2002 editions
> of
> > 13 & 72 here.
> 
> > On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72 states that
> > the air supervisory sensor shall signal on loss of 10 PSI but also on 10
> PSI
> > greater than the system set pressure.  Check out 5.13 for yourself but I'm
> > thinking Ive never seen or tested for air greater than 10 PSI of the set
> > pressure before.
> 
> > How is this being handled in the field during installs and maintenance ?
> > Does the typical air pressure switch in the little red cover actually
> cover
> > both loss and increase pressures?
> 
> > Thanks.
> 
> > Dave - a NJ AHJ
> 
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> > To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> 
> 
> -- 
> Best regards,
>  Charles                            mailto:[EMAIL PROTECTED]
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to