When you have 25 or 30 seconds to bring the end heads up to operating
pressure, the QRS isn't expensive- it's
P R I C E L E S S 

Let's face it, how else can you reliably trip a system in 3.5 seconds?

There had to be a better way than the flying saucers that were shot after
you trip test the original installation. And here it is.

I'm still amazed how you can massage a system with the FTD calcs and even
sleep well the night before trip testing a 1200+ gallon system. Quite a
change from showing up with an accelerator, exhauster, 2nd DPV and 250' of
6" galv in case you don't hit yer 60 seconds. I don't miss those days a bit.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Wednesday, October 24, 2007 6:53 AM
To: [email protected]
Subject: RE: Supervisory Alarm - Low Air

Have you seen what those are going for?  Man!

Tom
Go Red Sox!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!


Good point- especially in the low tolerance Potter QRS, so ya don't lunch it
!

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Wednesday, October 24, 2007 3:56 AM
To: [email protected]
Subject: RE: Supervisory Alarm - Low Air

And a bleeder valve for testing/setting, like you would with any pressure
switch monitoring (high-low not null, like PS-10's).  I've had pretty good
luck with the standard Ashcroft 1005 series 3-2-3 gauges, 0-80 w/retard.  5
year life cycle per #25.
We've cut them into the main rather than at the dry pipe valve.  Must the
gauge be listed?  I always thought so.
Tom


Just a word of caution regarding low differential DPV supervisory air or any
critical low air alarm. Always use a calibrated test gauge to set the
pressure switch. Trying to find 7 PSI on a the best gauge that $5.00 can buy
will always be a challenge. At one time some of the valves came with gauges
with 0-300 lb scales . . . a standard trim gauge. . .  in my view not
suitable for the application. A good gauge with a scale of 0-50 lb would be
a worthwhile investment when dealing with such low pressures.

Mike Cabral