Thom, I respectfully disagree with your assertion that, "The flat spray pattern will have most of the water hitting the side of the soffit and dropping to the floor without ever wetting the wall". If the spray pattern is this flat the water will never reach the floor except where it hits the wall. While the spray pattern is flat, it is also one that sprays downward and even slightly backward. Looking at the diagrams given in 13, the one for the "beam rule" never shows a wall directly behind the obstruction. The reason for this would be the very obvious, at least to me, intent that an obstruction that is a distance away from the wall will block the spray pattern and impede wall wetting. While an obstruction directly against the wall would not inhibit wall wetting to the same degree, especially one as small as 12" x 12". Again, I see that good judgment needs to be used because if this same soffit were 36" x 36" I would place a sprinkler in it.
Respectfully, Bob Knight -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Tuesday, October 30, 2007 10:06 AM To: [email protected] Subject: Re: Residental Sidewall Soffit Obstruction When you apply criteria for upright and pend sprinklers to HSW sprinklers your doing more than splitting hairs you bastardizing the standard. If your using a Residential Sidewall sprinkler, look at the obstruction rules for a Residential Sidewall Sprinkler! The reason a soffitt against the opposite wall is a problem for residential sidewall heads is because of the flat spray pattern, and the need for wall wetting. The flat spray pattern will have most of the water hitting the side of the soffit and dropping to the floor without ever wetting the wall, if you don't follow 8.10.7.1.3. While we have definitions for "Obstructed construction" We don't have one for Obstruction. I believe that in our use of the word, an obstruction is anything which prevents or inhibits the sprinkler discharge or spray pattern from developing and providing the same properties as when that condition is not present. If a soffit is low enough for the spray from a HSW to hit it, it will prevent wall wetting, and disrupt the development of the spray pattern that would be developed if it were not present. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "Dyce Geoffrey H." <[EMAIL PROTECTED]> To: <[email protected]> Sent: Tuesday, October 30, 2007 6:31 AM Subject: RE: Residental Sidewall Soffit Obstruction I think we are really splitting hairs on this. Is the soffit against the wall really an obstruction? I can read NFPA and don't get this one. There is nothing on the other side of the soffit but the wall. Although Figure 8.10.6.1.2(b) is for upright and pendent sprinklers, it appears to be the only thing that addresses obstructions against walls. The key word is against walls. I cant believe a 1-0 x 1-0 soffit against a far wall has any bearing as an obstruction to a spray pattern from a sidewall on the opposite wall. If this is the case, I guess we also have to consider the wall as an obstruction to the spray pattern. Must be a rule for this somewhere. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Monday, October 29, 2007 3:56 PM To: [email protected] Subject: Re: Residental Sidewall Soffit Obstruction There are listed residential HSW sprinkler heads that can be mounted 12' down from the ceiling. if these heads are installed there would not be an issue with a soffitt that is only 12 " deep on the opposite wall. If you are using any other placement location for the HSW then you will have to meet the rules of Table 8.10.7.1.3 "Positioning of sprinklers to avoid obstructions (residential sidewall sprinklers) This is as directed 8.10.7.1.3 for obstructions more than 8'-0" from the sprinkler----. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 ----- Original Message ----- From: "R Richardson" <[EMAIL PROTECTED]> To: <[email protected]> Sent: Monday, October 29, 2007 11:40 AM Subject: Residental Sidewall Soffit Obstruction Is the intent of NFPA 13 to treat a soffit on the opposite wall from which a residential sprinkler head is installed as a beam with respect to obstruction to spray pattern? Or can one ignore the area under the soffitt. The case we have is a 1 ft. deep soffit along the wall opposite from the wall where the residential sidewall head is mounted. A straight NFPA 13 application sends one to the beam rule, which requires the head to head to be at least 14 ft. away, but it is only 10 ft. away. So does one really have to install a head under the 1 x 1 ft. soffit on the opposite side of the room where the sidewall head is located? Note: 2007 NFPA 13 section 8.7.5.1.5 for standard sidewall heads has an allowance to ignore the soffit on the opposite wall, but this is the only place we can find this situation addressed. Thanks, Rich Richardson Seattle Fire Department _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.503 / Virus Database: 269.15.13/1099 - Release Date: 10/30/2007 10:06 AM No virus found in this outgoing message. Checked by AVG Free Edition. Version: 7.5.503 / Virus Database: 269.15.13/1099 - Release Date: 10/30/2007 10:06 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)