It is a new pump under subject to acceptance test.
The RPM varies 5% around the name plate 1750 RPM.
It is essentially- sea level. 

It seems that under the NFPA 10% allowance i.r.o. RPM, the Name Plate has a
limited meaning. 

I assume that this is the impact of the suppliers on the standards, not that
of the customers. 

Don't rely on NFPA/UL/FM.  Upon purchasing, specify the desirable operating
range. 

Dan  



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: 30 October, 2007 12:37 PM
To: [email protected]
Subject: RE: Fire Pump performance as per the name plate

Elevation?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Tuesday, October 30, 2007 6:22 AM
To: [email protected]
Subject: RE: Fire Pump performance as per the name plate

Is this a new pump?  Under factory warrantee?
To be accepted, it has to meet nameplate.  If it didn't, why specify?
New pump, you have a beef.  Old pump, time to make some changes.
Nameplate RPM is at 150%, not churn or design.  Is rpm within the range of
the driver?
Sounds like someone needs a PRV.
Tom


Dear All,

I have got a problem with a fire pump.

The pump performance does not match the name plant data.

The cause is the Diesel Engine.

The engine RPM deviation from "No Load" to 150% nominal is 90 rpm, just over
5% of the nominal (1760 rpm).

The result is too high pressure (5% excess) at churning causing operation of
the 175psi relief valves of the sprinkler systems,

At the other end, 150% flow, the pressure is 5% below the name plant data.

The question: To what extent the pump supplier is bound by the name plant
performance data.

The supplier Rep. argues that 5% deviation is within the normal.


Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to