8.10.7.1.5 Refers to soffits that are used for the installation of sprinklers and references 8.10.7.1.5.1 which says to install sprinklers under soffits wider than 8". I have been told in at least two different seminars that 8.10.7.1.5.1 refers specifically to the soffit the sprinkler is mounted in. 8.10.7.1.5.2 and 8.10.7.1.5.3 then goes on to exclude sprinklers under soffits up to 12" in width with cabinets mounted to the bottom of them.

Sorry about the 28" vs. 32" I haven't had to deal with that since I left Star in 93.

Richard L. Mote CET
Designer
Rowe Sprinkler Systems, Inc




----- Original Message ----- From: "Thom McMahon" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, October 30, 2007 1:42 PM
Subject: Re: Residental Sidewall Soffit Obstruction


Actually UL 7-12-02 is "One or more sprinklers must wet the wall within 28" of the ceiling" The effect on a sidewall will be greater the closer to the head the soffit is located. In a situation where the wall is 16'-0" from the head the 1'-0" soffit has no effect, but because the MINIMUM for a res. HSW is 12x12 something on a 10'-0" wall sticking out 1"-0" will have greater impact. (Again see Table 8.10.7.1.3) The fact that this soffit is 12'' down and 12" wide, makes all of this discussion moot, since you must comply with 8.10.7.1.5.1, if 8.10.7.1.3 doesn't work for you.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Richard Mote" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, October 30, 2007 10:41 AM
Subject: Re: Residental Sidewall Soffit Obstruction


Residential sprinklers are only required to wet the far wall to within 32" (if memory serves) of the ceiling to obtain a listing. The only manufacturer I could find that still publishes spray patterns (I stopped looking when I
found these) is Victaulic. Their V2738 K4.2 @ 14gpm @ 4" down from the
ceiling in a 12' x 12' room wets the far wall to just about a foot down from
ceiling. So it would seem that a 1'x1' soffit against the far wall would
have little or no impact on coverage. I believe 8.10.7.1.3 (07) is referring to obstructions away from the wall such as ceiling beams or other continuous
obstructions. The reason I feel this way is that the opposite wall is not
required to be wetted all the way to the ceiling to obtain a listing.
Therefore any soffit, curtain valance or other construct that would be
against the far wall in the area not required to be wetted would have no
effect on spray pattern..

Or I could be suffering from advanced old timers disease.

Richard L. Mote CET
Designer
Rowe Sprinkler Systems, Inc





----- Original Message ----- From: "Dyce Geoffrey H." <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, October 30, 2007 8:31 AM
Subject: RE: Residential Sidewall Soffit Obstruction


I think we are really splitting hairs on this.  Is the soffit against the
wall really an obstruction? I can read NFPA and don't get this one. There
is nothing on the other side of the soffit but the wall.  Although Figure
8.10.6.1.2(b) is for upright and pendent sprinklers, it appears to be the
only thing that addresses obstructions against walls.  The key word is
against walls. I cant believe a 1-0 x 1-0 soffit against a far wall has any bearing as an obstruction to a spray pattern from a sidewall on the opposite wall. If this is the case, I guess we also have to consider the wall as an
obstruction to the spray pattern.  Must be a rule for this somewhere.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Monday, October 29, 2007 3:56 PM
To: [email protected]
Subject: Re: Residental Sidewall Soffit Obstruction

There are listed residential HSW sprinkler heads that can be mounted 12'
down from the ceiling. if these heads are installed there would not be an
issue with a soffitt that is only 12 " deep on the opposite wall.
If you are using any other placement location for the HSW then you will have
to meet the rules of Table 8.10.7.1.3 "Positioning of sprinklers to avoid
obstructions (residential sidewall sprinklers) This is as directed
8.10.7.1.3 for obstructions more than 8'-0" from the sprinkler----.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "R Richardson" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, October 29, 2007 11:40 AM
Subject: Residental Sidewall Soffit Obstruction


Is the intent of NFPA 13 to treat a soffit on the opposite wall from which a
residential sprinkler head is installed as a beam with respect to
obstruction to spray pattern? Or can one ignore the area under the soffitt.

The case we have is a 1 ft. deep soffit along the wall opposite from the
wall where the residential sidewall head is mounted.   A straight NFPA 13
application sends one to the beam rule, which requires the head to head to
be at least 14 ft. away, but it is only 10 ft. away.  So does one really
have to install a head under the 1 x 1 ft. soffit on the opposite side of
the room where the sidewall head is located?

Note: 2007 NFPA 13 section 8.7.5.1.5  for standard sidewall heads has an
allowance to ignore the soffit on the opposite wall, but this is the only
place we can find this situation addressed.

Thanks,

Rich Richardson
Seattle Fire Department

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to