With one except, you are absolutely correct that they are two
different types of sprinklers with two different design criteria.
How would one mix the assignment of the size of a remote area within
one compartment? So if it is done twice, does a double negative make
it a positive????
The exception is that mechanical closets can use a QR SPRAY sprinkler
and I would also argue the IBC required balcony is enough of a
separate area to treat independently.
Roland
On Dec 12, 2007, at 2:29 PM, Dewayne Martinez wrote:
NFPA 13R 07 ed
I see that 6.7.7.1.3 allows us to use QR sprinklers in a dwelling unit
as long as there is no more that 4 QR sprinklers in the compartment
and
we calc the compartment at a 0.1 over the entire compartment.
We have been asked to design a building typical to the way another
contractor did it by installing a QR dry pnd off the dry system and
RES
hsw in the same compartment. I was always under the impression
that you
could not mix the two types in the same compartment. Am I wrong?
Thanks,
Dewayne