Just to clarify. You are permitted to use QR only when the total number of 
sprinklers in the DWELLING UNIT does not exceed four. If the DWELLING UNIT 
contains five sprinklers or more, then you are forced to use residential 
sprinklers. 
   
  Scott Mitchell

Dewayne Martinez <[EMAIL PROTECTED]> wrote:
  NFPA 13R 07 ed
I see that 6.7.7.1.3 allows us to use QR sprinklers in a dwelling unit
as long as there is no more that 4 QR sprinklers in the compartment and
we calc the compartment at a 0.1 over the entire compartment.
We have been asked to design a building typical to the way another
contractor did it by installing a QR dry pnd off the dry system and RES
hsw in the same compartment. I was always under the impression that you
could not mix the two types in the same compartment. Am I wrong? 
Thanks,
Dewayne