The restriction of the number of QR heads in a compartment was in the code
for a long time. I think ever since the advent of the QR sprinkler and it
applied to BOTH inside & outside dwelling units. From what I understand this
restriction is to limit the number of sprinklers being activated. If that
was the concern, why is there no restriction for non-residential QR
applications, such as mandatory light hazard use?

Also I can see a restriction when the design number of sprinklers is four.
Shouldn't more than four be permitted if all heads in the compartment was
calculated?

Tony 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of scott
mitchell
Sent: December 12, 2007 8:43 PM
To: [email protected]
Subject: Re: Mixing QR and RES sprinklers in a unit

Just to clarify. You are permitted to use QR only when the total number of
sprinklers in the DWELLING UNIT does not exceed four. If the DWELLING UNIT
contains five sprinklers or more, then you are forced to use residential
sprinklers. 
   
  Scott Mitchell

Dewayne Martinez <[EMAIL PROTECTED]> wrote:
  NFPA 13R 07 ed
I see that 6.7.7.1.3 allows us to use QR sprinklers in a dwelling unit as
long as there is no more that 4 QR sprinklers in the compartment and we calc
the compartment at a 0.1 over the entire compartment.
We have been asked to design a building typical to the way another
contractor did it by installing a QR dry pnd off the dry system and RES hsw
in the same compartment. I was always under the impression that you could
not mix the two types in the same compartment. Am I wrong? 
Thanks,
Dewayne

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


       
---------------------------------
Never miss a thing.   Make Yahoo your homepage.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to