1)Our usual practice for us is to put the control valve in the stairwell with the hose valves on the roof but we now have one AHJ that requires the control valve on the roof like the detail shown in the appendix of 14. 2)I don't remember seeing anything specifying the location in 14. 3)Depends on the AHJ, we do it both ways here.
Dewayne Martinez Design Build Fire Protection [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, January 08, 2008 5:25 PM To: [email protected] Subject: Standpipes - Location of Class I Hose Connections 7.3.2.5 At the highest landing of stairways with stairway access to a roof, and on the roof where stairways do not access the roof. 1. Must there be a valve on roof when there is no hatch, ladder, door, nada? 2. If yes to #1 can the valve be located anywhere on the roof? 3. Where there are two stairs and one has a roof access door and the valve is within 200 ft. of the all parts of the roof, must a valve be extended through the roof from the standpipe with no roof access? Thanks, Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)