IN 14, 2007 THE NEXT PARAGRAPH SAYS A PRV IS EQUIVALENT TO A CHECK.
Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Peter Nadhazy
Sent: Friday, February 15, 2008 8:38 AM
To: [email protected]
Subject: Check valve on floor control assembly
If the system is a combination standpipe and sprinkler system NFPA
14 6.2.5
states "each connection to the sprinkler system shall have an
individual
control valve and check valve of the same size as the connection".
Si it is
usually not a big deal to provide and also makes it easier to test
large
systems.
VTY,
Peter Nadhazy Cell (508)493-3933
Marathon Fire Protection, Inc.
578 Arcade Avenue
PO BOX 160
Seekonk, MA 02771
(508)336-4300
Fax :(508)336-4232
email: [EMAIL PROTECTED]
www.marathonfire.com
----- Original Message -----
From: "Roland Huggins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, February 14, 2008 11:53 AM
Subject: Re: Check valve on floor control assembly
> We ALL think that but 13 is a tad weak on addressing high rises
except
> for combined sprinkler standpipes (so in a back door manner
catches
> most). 13 addresses two items:
>
> Where each sprinkler system on each floor is equipped with a
separate
> water flow device, it shall be connected to an alarm system etc
etc.
> Doesn't say you have to provide the thing.
>
> It's also amusing that the floor control valve in Figure A.
8.17.4.2 (b is
> not discussed in that section of the body. Actually 8.16.1.1.2.2
> mentions the floor control valve by saying that it will be
supervised per
> 8.16.1.1.2.1. Doesn't say you have to have it. As already
identified,
> the building code takes care of that.
>
> It is one of those things that most of us have always done and
think it
> must be cleanly addressed in 13 (until you actually look at).
This is
> just like the requirement for having a check valve in every
riser. You
> won't find that either.
>
> LIke a few other things, since no one is submitting proposals
on it, it
> isn't on the radar screen of the TC.
>
> Roland
>
> On Feb 14, 2008, at 7:54 AM, Ed Kramer wrote:
>
>> Cliff, I'm not aware of anything in 13 that requires the check
valve.
>> Also worth noting, nothing in 13 requires that each floor has
its own control
>> valve (except for high rises, I think). I tried to find the
section
>> that requires the control valves in high rises but couldn't.
Anyone know if
>> it's been removed, or am I just missing it?
>>
>> Ed Kramer
>> Littleton, CO
>>
>>> -----Original Message-----
>>> From: [EMAIL PROTECTED]
[mailto:sprinklerforum-
>>> [EMAIL PROTECTED] On Behalf Of Cliff Whitfield
>>> Sent: Wednesday, February 13, 2008 1:50 PM
>>> To: [email protected]
>>> Subject: Check valve on floor control assembly
>>>
>>> NFPA 14 requires a check valve on a floor control assembly for a
>>> connection to a standpipe that is part of a combined system.
(6.3.5.1 2007 ed)
>>> Does this requirement cross over to NFPA 13 for a riser in a
multi-story
>>> building that is not actually a standpipe? Like for a 3-story
bldg that isn't
>>> high enough to require a standpipe.
>>>
>>>
>>>
>>> I understand that it would be a good idea for the same reasons
it is
>>> required on a standpipe but is it actually a requirement?
>>>
>>>
>>>
>>> Cliff Whitfield, SET
>>>
>>> Fire Design, Inc.