Point taken, thanks.
Bill Minkel, Designer Western States Fire Protection, Dallas NFPA Member #2578666 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Monday, February 18, 2008 10:31 AM To: [email protected] Subject: Re: Check valve on floor control assembly Be careful with the casual use of PRV since there are three different types. On Feb 15, 2008, at 6:34 PM, Frans Stoop wrote: > There is at least one Pressure Reducing Valve (Bermad model FP720- > UL) that steers open when the upstream pressure drops below downstream > pressure. > The consequence is that for example, you can't use this PRV on the > pressure side of a fire pump and leave the regular check valve out. > (This PRV is UL-listed!) > > I don't know exactly about other PRV brands, but their principle of > operation looks very much like the Bermad. > > Frans Stoop > > At 14:35 15-2-2008 -0600, you wrote: >> IN 14, 2007 THE NEXT PARAGRAPH SAYS A PRV IS EQUIVALENT TO A CHECK. >> >> Bill Minkel, Designer >> Western States Fire Protection, Dallas NFPA Member #2578666 >> >> -----Original Message----- >> From: [EMAIL PROTECTED] >> [mailto:[EMAIL PROTECTED] On Behalf Of Peter >> Nadhazy >> Sent: Friday, February 15, 2008 8:38 AM >> To: [email protected] >> Subject: Check valve on floor control assembly >> >> If the system is a combination standpipe and sprinkler system NFPA >> 14 6.2.5 >> states "each connection to the sprinkler system shall have an >> individual control valve and check valve of the same size as the >> connection". >> Si it is >> usually not a big deal to provide and also makes it easier to test >> large systems. >> VTY, >> Peter Nadhazy Cell (508)493-3933 >> Marathon Fire Protection, Inc. >> 578 Arcade Avenue >> PO BOX 160 >> Seekonk, MA 02771 >> (508)336-4300 >> Fax :(508)336-4232 >> email: [EMAIL PROTECTED] >> www.marathonfire.com >> >> ----- Original Message ----- >> From: "Roland Huggins" <[EMAIL PROTECTED]> >> To: <[email protected]> >> Sent: Thursday, February 14, 2008 11:53 AM >> Subject: Re: Check valve on floor control assembly >> >> >> > We ALL think that but 13 is a tad weak on addressing high rises >> except >> > for combined sprinkler standpipes (so in a back door manner >> catches >> > most). 13 addresses two items: >> > >> > Where each sprinkler system on each floor is equipped with a >> separate >> > water flow device, it shall be connected to an alarm system etc >> etc. >> > Doesn't say you have to provide the thing. >> > >> > It's also amusing that the floor control valve in Figure A. >> 8.17.4.2 (b is >> >> > not discussed in that section of the body. Actually 8.16.1.1.2.2 >> > mentions the floor control valve by saying that it will be >> supervised per >> >> > 8.16.1.1.2.1. Doesn't say you have to have it. As already >> identified, >> > the building code takes care of that. >> > >> > It is one of those things that most of us have always done and >> think it >> > must be cleanly addressed in 13 (until you actually look at). >> This is >> > just like the requirement for having a check valve in every >> riser. You >> > won't find that either. >> > >> > LIke a few other things, since no one is submitting proposals >> on it, it >> > isn't on the radar screen of the TC. >> > >> > Roland >> > >> > On Feb 14, 2008, at 7:54 AM, Ed Kramer wrote: >> > >> >> Cliff, I'm not aware of anything in 13 that requires the check >> valve. >> >> Also worth noting, nothing in 13 requires that each floor has >> its own control >> >> valve (except for high rises, I think). I tried to find the >> section >> >> that requires the control valves in high rises but couldn't. >> Anyone know if >> >> it's been removed, or am I just missing it? >> >> >> >> Ed Kramer >> >> Littleton, CO >> >> >> >>> -----Original Message----- >> >>> From: [EMAIL PROTECTED] >> [mailto:sprinklerforum- >> >>> [EMAIL PROTECTED] On Behalf Of Cliff Whitfield >> >>> Sent: Wednesday, February 13, 2008 1:50 PM >> >>> To: [email protected] >> >>> Subject: Check valve on floor control assembly >> >>> >> >>> NFPA 14 requires a check valve on a floor control assembly for a >> >>> connection to a standpipe that is part of a combined system. >> (6.3.5.1 2007 ed) >> >>> Does this requirement cross over to NFPA 13 for a riser in a >> multi-story >> >>> building that is not actually a standpipe? Like for a 3-story >> bldg that isn't >> >>> high enough to require a standpipe. >> >>> >> >>> >> >>> >> >>> I understand that it would be a good idea for the same reasons >> it is >> >>> required on a standpipe but is it actually a requirement? >> >>> >> >>> >> >>> >> >>> Cliff Whitfield, SET >> >>> >> >>> Fire Design, Inc. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] (Put the word unsubscribe in the subject > field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)