Point taken, thanks. 

Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, February 18, 2008 10:31 AM
To: [email protected]
Subject: Re: Check valve on floor control assembly

Be careful with the casual use of PRV since there are three different types.
On Feb 15, 2008, at 6:34 PM, Frans Stoop wrote:

> There is at least one Pressure Reducing Valve (Bermad model FP720-
> UL) that steers open when the upstream pressure drops below downstream 
> pressure.
> The consequence is that for example, you can't use this PRV on the 
> pressure side of a fire pump and leave the regular check valve out.
> (This PRV is UL-listed!)
>
> I don't know exactly about other PRV brands, but their principle of 
> operation looks very much like the Bermad.
>
> Frans Stoop
>
> At 14:35 15-2-2008 -0600, you wrote:
>>  IN 14, 2007 THE NEXT PARAGRAPH SAYS A PRV IS EQUIVALENT TO A CHECK.
>>
>> Bill Minkel, Designer
>> Western States Fire Protection, Dallas NFPA Member #2578666
>>
>> -----Original Message-----
>> From: [EMAIL PROTECTED]
>> [mailto:[EMAIL PROTECTED] On Behalf Of Peter 
>> Nadhazy
>> Sent: Friday, February 15, 2008 8:38 AM
>> To: [email protected]
>> Subject: Check valve on floor control assembly
>>
>> If the system is a combination standpipe and sprinkler system NFPA
>> 14 6.2.5
>> states "each connection to the sprinkler system shall have an 
>> individual control valve and check valve of the same size as the 
>> connection".
>> Si it is
>> usually not a big deal to provide and also makes it easier to test 
>> large systems.
>> VTY,
>> Peter Nadhazy Cell (508)493-3933
>> Marathon Fire Protection, Inc.
>> 578 Arcade Avenue
>> PO BOX 160
>> Seekonk, MA 02771
>> (508)336-4300
>> Fax :(508)336-4232
>> email: [EMAIL PROTECTED]
>> www.marathonfire.com
>>
>> ----- Original Message -----
>> From: "Roland Huggins" <[EMAIL PROTECTED]>
>> To: <[email protected]>
>> Sent: Thursday, February 14, 2008 11:53 AM
>> Subject: Re: Check valve on floor control assembly
>>
>>
>> > We ALL think that but 13 is a tad weak on addressing high rises   
>> except
>> > for combined sprinkler standpipes (so in a back door manner   
>> catches
>> > most).   13 addresses two items:
>> >
>> > Where each sprinkler system on each floor is equipped with a
>> separate
>> > water flow device, it shall be connected to an alarm system etc
>> etc.
>> > Doesn't say you have to provide the thing.
>> >
>> > It's also amusing that the floor control valve in Figure A. 
>> 8.17.4.2 (b  is
>>
>> > not discussed in that section of the body.  Actually  8.16.1.1.2.2 
>> > mentions the floor control valve by saying that it will  be
>> supervised per
>>
>> > 8.16.1.1.2.1.  Doesn't say you have to have it.  As  already
>> identified,
>> > the building code takes care of that.
>> >
>> > It is one of those things that most of us have always done and
>> think  it
>> > must be cleanly addressed in 13 (until you actually look at).     
>> This is
>> > just like the requirement for having a check valve in every   
>> riser.  You
>> > won't find that either.
>> >
>> > LIke a few other things, since no one is submitting  proposals
>> on it,  it
>> > isn't on the radar screen of the TC.
>> >
>> > Roland
>> >
>> > On Feb 14, 2008, at 7:54 AM, Ed Kramer wrote:
>> >
>> >> Cliff, I'm not aware of anything in 13 that requires the check   
>> valve.
>> >> Also worth noting, nothing in 13 requires that each floor has
>> its own  control
>> >> valve (except for high rises, I think).  I tried to find the   
>> section
>> >> that requires the control valves in high rises but couldn't.   
>> Anyone  know if
>> >> it's been removed, or am I just missing it?
>> >>
>> >> Ed Kramer
>> >> Littleton, CO
>> >>
>> >>> -----Original Message-----
>> >>> From: [EMAIL PROTECTED]   
>> [mailto:sprinklerforum-
>> >>> [EMAIL PROTECTED] On Behalf Of Cliff Whitfield
>> >>> Sent: Wednesday, February 13, 2008 1:50 PM
>> >>> To: [email protected]
>> >>> Subject: Check valve on floor control assembly
>> >>>
>> >>> NFPA 14 requires a check valve on a floor control assembly for a 
>> >>> connection to a standpipe that is part of a combined system.
>> (6.3.5.1 2007 ed)
>> >>> Does this requirement cross over to NFPA 13 for a riser in a
>> multi-story
>> >>> building that is not actually a standpipe?  Like for a 3-story
>> bldg that isn't
>> >>> high enough to require a standpipe.
>> >>>
>> >>>
>> >>>
>> >>> I understand that it would be a good idea for the same reasons
>> it is
>> >>> required on a standpipe but is it actually a requirement?
>> >>>
>> >>>
>> >>>
>> >>> Cliff Whitfield, SET
>> >>>
>> >>> Fire Design, Inc.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
> field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to