Consider the breakdown of H2SO4

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: 16 February, 2008 6:51 PM
To: [email protected]
Subject: Re: MIC causing fire??

When the aerobic bacteria take their oxygen out of the water do they
use free oxygen or do they break down the water? If the later what
happens to the left over hydrogen? Is it combined with something else
to form another inert compound? Is it dissolved in the water (my
wording may be incorrect since my chemistry is pretty much limited to
making incendiaries and explosives from household chemicals)? Is it
free and could it migrate to a single point in sufficient quantity to
cause the flash Frans described? Could it merely have been cutting
oils or other manufacturing by-products ignited by the welder?

On Feb 16, 2008 5:37 AM, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote:
> Bacteria by themselves, to my knowledge, do not burn. And their waste
> products are acids. (My father was a bacteriologist and I'm going
> back a few years on this) Bacteria do, however, help decompose
> organic matter, by-products of which could be combustible (i.e.
> methane from cows). If the foam was organic, then that possibility
> could exist. I would highly doubt that reaction could come from a wet
> or dry system. Was this fed by potable water? If it came from an open
> source, there might be sufficient organics to create some decomposition.
>
>
>
>
> At 07:52 AM 2/16/2008, you wrote:
> >Gregg,
> >
> >I think it was a wet pipe system. But does it make a difference?
> >I think the question comes down to: "Do MIC-bacteria produce
> >combustible gases?"
> >
> >Frans Stoop
> >
> >At 13:04 15-2-2008 -0500, you wrote:
> >>Fran, Which of the 3 systems did the welding crew cut? Gregg
> >>
> >>Frans Stoop wrote:
> >>>Dear colleagues,
> >>>A plant owner has a new sprinkler system. Installation started 2
> >>>years ago. Final acceptance was approx. 6 month ago. All sprinkler
> >>>piping is (interior and exterior) hot dip galvanized steel. Some
> >>>systems are dry, some are wet and some contain water + 1%
AFFF-concentrate.
> >>>A few month ago a mechanial crew was welding some process piping
> >>>and accidentally cut a sprinkler pipe.
> >>>The mechanics claim that a flash flame came out of the sprinkler pipe!
> >>>This caused some disturbance as you can imagine.
> >>>An investigation is going on since.
> >>>Recently someone with a lab told our client that MIC bacteria may
> >>>have produced combustible gas that could have been collected in
> >>>the sprinkler pipe.
> >>>Question: is there any chance that this can be true?
> >>>Or should we look for another cause?
> >>>Frans Stoop
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.20.6/1282 - Release Date: 15-Feb-08
7:08 PM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.516 / Virus Database: 269.20.6/1282 - Release Date: 15-Feb-08
7:08 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to