I feel certain that this is not what the code intends. In the case you
describe we would consider it Ord. Hazard and calculate it as one room
without omitting the heads.
In virtually all of the cases like this we have seen, the owner has put
chainlink over the tops of the closets and held the walls down to keep the
deflectors 18" above them.
Have a great weekend,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Friday, February 22, 2008 4:05 PM
To: [email protected]
Subject: Gaggle of closets

I am looking an apartment building which is to be designed according 
to NFPA 13. On the first level, there is a room which contains 55 - 
3'x5' tenant storage closets (mostly filled with shelves). These 
would need to be sprinklered, which is fine, but the issue comes in 
the hydraulics. Section 14.4.4.4.2 states that closets with a single 
sprinkler may be omitted from the calculation. There could be up to 
47 closets in the remote area. I have used this exception numerous 
times, but never in this quantity. The standard says nothing to the 
contrary, so I could eliminate 47 sprinklers in the remote area 
because they are in closets? Is there something I am overlooking?



Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to