Don't you just love it when the letter of the code works in your favor.
I really don't think that this is what the NFPA 13 committee had in mind
when they developed that section.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, February 22, 2008 5:05 PM
To: [email protected]
Subject: Gaggle of closets

I am looking an apartment building which is to be designed according 
to NFPA 13. On the first level, there is a room which contains 55 - 
3'x5' tenant storage closets (mostly filled with shelves). These 
would need to be sprinklered, which is fine, but the issue comes in 
the hydraulics. Section 14.4.4.4.2 states that closets with a single 
sprinkler may be omitted from the calculation. There could be up to 
47 closets in the remote area. I have used this exception numerous 
times, but never in this quantity. The standard says nothing to the 
contrary, so I could eliminate 47 sprinklers in the remote area 
because they are in closets? Is there something I am overlooking?



Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to