Chris,

Don't be so quick to jump to that conclusion. Another case of it says this or it doesn't say that so I can do it. I think you should be very careful here. Dig a little deeper and get to the logical intent, and not just what it says or doesn't say in black and white.

This is an area separate from the dwelling areas, and is likely to be crammed full of who knows what. In addition, there is no mention of wall or ceiling contruction (which could affect one's direction on this issue).

I agree with Greg that this is not likely what the NFPA standard committee intends for this exception.

In reading the commentary in the Automatic Sprinkler Systems Handbook on this issue, I believe there is merit to the fact that the standards committee intended small rooms to mean small light hazard/low fuel load rooms. This would not seem to be low fuel loading, and is not, in my opinion, is an ordinary hazard area rather than light hazard. And because it's storage, and you don't know what could go in there, OH1 ain't good enough, it needs to be OH2.

Just my opinion



Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)

This e-mail and any attachments are CONFIDENTIAL and may be protected by one or more legal privileges. It is intended solely for the use of the addressee identified above. If you are not the intended recipient, any use, disclosure, copying or distribution of this e-mail is unauthorized. If you received this e-mail in error, please notify the sender immediately at the above captioned address. ----- Original Message ----- From: "Chris Mak" <[EMAIL PROTECTED]>
To: "sprinklerforum" <[email protected]>
Sent: Friday, February 22, 2008 4:40 PM
Subject: Re: Gaggle of closets


Could you foresee a fire senario where the 47 extra heads would operate. I think that this is exactly what the exception is for.

Regards


----- Original Message -----
From: "Paul Pinigis" [EMAIL PROTECTED]
Sent: 22/02/2008 05:30 PM EST
To: <[email protected]>
Subject: RE: Gaggle of closets



Don't you just love it when the letter of the code works in your favor.
I really don't think that this is what the NFPA 13 committee had in mind
when they developed that section.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, February 22, 2008 5:05 PM
To: [email protected]
Subject: Gaggle of closets

I am looking an apartment building which is to be designed according
to NFPA 13. On the first level, there is a room which contains 55 -
3'x5' tenant storage closets (mostly filled with shelves). These
would need to be sprinklered, which is fine, but the issue comes in
the hydraulics. Section 14.4.4.4.2 states that closets with a single
sprinkler may be omitted from the calculation. There could be up to
47 closets in the remote area. I have used this exception numerous
times, but never in this quantity. The standard says nothing to the
contrary, so I could eliminate 47 sprinklers in the remote area
because they are in closets? Is there something I am overlooking?



Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


This document should only be read by those persons to whom it is addressed and is not intended to be relied upon by any person without subsequent written confirmation of its contents. Accordingly, our company disclaim all responsibility and accept no liability (including in negligence) for the consequences for any person acting, or refraining from acting, on such information prior to the receipt by those persons of subsequent written confirmation.

If you have received this e-mail message in error, please notify us immediately by telephone. Please also destroy and delete the message from your computer. The Unsolicited Electronic Message Act 2007 (The Spam Act) came into effect from 5 September 2007. As a valued client you may receive communications from us from time to time, including electronic publications, invitations and related information. Please advise if you wish us to stop sending these communications to you. Otherwise we will assume you wish to continue receiving these communications from us.

Any form of reproduction, dissemination, copying, disclosure, modification, distribution and/or publication of this e-mail message is strictly prohibited.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to