I think you have to ask yourself, Do you feel lucky?  No, that's something
completely different.  Let's try another one, How many sprinklers would you
foresee operating in any given fire?  A fire originating in one of the
closets is going to get drowned by the sprinkler inside the closet, so that
sprinkler and maybe 2 others in the hall.  A fire originating in the hall -
at least 5 in the hall and however many more it takes to makes you feel
comfortable.  If the total number of DA sprinklers in 900 sf (not including
those in closets) exceeds the numbers from above, then you likely can use
the closet loophole and still sleep well at night (with or without the
flaming stress management).

Time for my flaming breakfast
Ed Kramer
Littleton, CO


> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC
> Sent: Friday, February 22, 2008 4:26 PM
> To: [email protected]
> Subject: Re: Gaggle of closets
> 
> The drawings that I have do not detail wall construction except that
> they will more than likely be sheetrock on stud walls and sheetrock
> ceilings. Also, the closets have 4 levels of shelves that take up
> most of the square footage. The issue here is that including the
> closets, there would be approximately 60 sprinklers in a 1500 sqft
> area and 40 in a 900 sqft area. Given that out square footage of each
> closet is 15 sqft and the minimum EHP is 7 psi, you will get a
> density of about 1 gpm/sqft from each head in the closet. OH1 vs OH2
> is irrelevant.