Hello Todd, Tyco flat spray
Sunday, February 24, 2008, 5:24:26 PM, you wrote: > K115 sprinkler? At 7 psi, it would discharge 304 gpm. That must be > one of those new FHO sprinklers. > At 04:47 PM 2/24/2008, you wrote: >>Hello Ed, >>How does the spec sheet on the Backflow min flow compare to the flow >>from a single sprinkler. K2.4 or K115 could be a difference also. >>Sunday, February 24, 2008, 4:14:58 PM, you wrote: >> > Will an eight-inch backflow preventer behave itself on the flow from a >> > single sprinkler? >> > Would a 4" be better? >>-- >>Best regards, >>Charles Thurston >> Coastal mailto:[EMAIL PROTECTED] >>_______________________________________________ >>Sprinklerforum mailing list >>[email protected] >>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >>To Unsubscribe, send an email to:[EMAIL PROTECTED] >>(Put the word unsubscribe in the subject field) > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, Connecticut > www.fpdc.com > 860.535.2080 > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) -- Best regards, Charles Thurston Coastal mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)