Hello Todd,

K115? Yes, of course, use them all the time. We in this small metrical country think big ;-).

Met vriendelijke groet / Yours sincerely,

Frans Stoop
TOS architecture & fire protection
Kingdom of the Netherlands

At 17:24 24-2-2008 -0500, you wrote:
K115 sprinkler? At 7 psi, it would discharge 304 gpm. That must be one of those new FHO sprinklers.

At 04:47 PM 2/24/2008, you wrote:
Hello Ed,

How does the spec sheet on the Backflow min flow compare to the flow from a single sprinkler. K2.4 or K115 could be a difference also.

Sunday, February 24, 2008, 4:14:58 PM, you wrote:

> Will an eight-inch backflow preventer behave itself on the flow from a
> single sprinkler?

> Would a 4" be better?

--
Best regards,
Charles Thurston
 Coastal                            mailto:[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to