Pardon moi, mon ami. Je ne pensais pas metrique. And I believe the Tyco Flat Spray is a metric sprinkler as well. (I think I got the first part right; it's been a long time)

At 07:03 PM 2/24/2008, you wrote:
Hello Todd,

K115? Yes, of course, use them all the time. We in this small metrical country think big ;-).

Met vriendelijke groet / Yours sincerely,

Frans Stoop
TOS architecture & fire protection
Kingdom of the Netherlands

At 17:24 24-2-2008 -0500, you wrote:
K115 sprinkler? At 7 psi, it would discharge 304 gpm. That must be one of those new FHO sprinklers.

At 04:47 PM 2/24/2008, you wrote:
Hello Ed,

How does the spec sheet on the Backflow min flow compare to the flow from a single sprinkler. K2.4 or K115 could be a difference also.

Sunday, February 24, 2008, 4:14:58 PM, you wrote:

> Will an eight-inch backflow preventer behave itself on the flow from a
> single sprinkler?

> Would a 4" be better?

--
Best regards,
Charles Thurston
 Coastal                            mailto:[EMAIL PROTECTED]