How about continue design so you don't lose your schedule, but advise you
are proceeding LH per their direction, and revisions will be a CO.

Can't you just ask the insur AHj to specify their criteria? Even a telecom
can be turned into a letter-in-reverse w/cc to A/E (or whomever your
contract is with) and note the requirement, confirm they want you to
continue as you've advised you would, on the basis of entire building LH.

If its #13, and I'd assume it would be, then the "sub-occupancies" would be
treated appropriate to their risk. Doesn't your state building code require
#13 as a minimum?

If design criteria were up to the owners maybe we could have installed that
system in a mattress place that kept having "hot buns" flaming up as LH as
the owner asked- we walked. It's not their call.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Sunday, February 24, 2008 5:38 PM
To: [email protected]
Subject: RE: Sprinklers in Art Bldg. at the University

The problem is what happens if the drawings come back from the A/E 
approved? I would assume that the insurance engineer would reject 
them, but can you really count on that? What would be your liability 
if everyone said go with the LH? The Owner, A/E and Insurance company 
need to hash this out. If it were me, I'd put a hold on the drawings 
until I get and answer (and put it in writing, of course). Keep 
pushing, you're doing the right thing.