The locked pressure is why you MUST have an expansion chamber. I think the Installation TC is looking favorable upon an APPROVED device instead of listed.

Back to your question. NFPA 13 does not require the use of a BFP. You can use either a BFP or the old loop and check valve with a hole. This does impact you since the water purveyor will require a BFP on the system (with a couple of exceptions). The rub is that typically a double check is used on the system whereas an RPZ is required for the chemical (they ignore that it's a non-toxic chemical). SO the question is do you want the RPZ on your system riser or your antifreeze connection? For those jurisdictions that require only RPZ's to be used on plain old wet pipe systems, why have two of them?

Roland

On Feb 26, 2008, at 2:16 PM, Brian wrote:

Aha! Well, that shoots down that theory...


Ron Greenman <[EMAIL PROTECTED]> wrote:
An RP does not permit the backward flow of water at all. On a RP if a
check completely fails then the dump port opens and water flows
forward through the dump port. If a drop in in line pressure occurs
then the dump port opens until the difference between line pressure
and system pressure is re-established. If all checks are holding the
anti-freeze expands against the second RP check as against any check
valve.

On 2/26/08, Brian
wrote:
Anyone see any problems with this: Having a 4" RP Backflow at the base of riser and then tapping an antifreeze system off of the wet system but instead of an expansion chamber (as required by code for a double check) running the old style a/f 5ft loop off of this. Reasoning is since an RP type backflow ports when overpressurized on system side the a/f system can still expand through the loop like in the good ol' days.

It seems NFPA#13 only requires the expansion chamber since it would be impossible for the antifreeze to otherwise expand since everything is 'locked' in place by the double check. However with an RP backflow it would allow the backwards movement of water neccessary for expansion and the loop would perform it's duties of acting as a container for the antifreeze and not be ported out with the water.

We had this arrangement ok'd by an AHJ in the past but want to see if there is something we're overlooking.

thx,




---------------------------------
Looking for last minute shopping deals? Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



---------------------------------
Looking for last minute shopping deals? Find them fast with Yahoo! Search.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to