As long as you're tapping into a 'wet' system, you're not required to have
the expansion chamber.  Section 7.5.3.1 ('02) should help clarify.  The idea
is that wet systems almost always contain some amount of air which is
compressible.  Small amounts of antifreeze can pass back through the hole in
the check valve and not over pressurize the wet system due to the air in the
wet system compressing.  Note that you're still allowed to have a BFP
(double-check or otherwise) as long as its not in the connection between the
wet system and the AFL.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Brian
> Sent: Tuesday, February 26, 2008 2:27 PM
> To: [email protected]
> Subject: RP Backflow with Antifreeze Loop
> 
> Anyone see any problems with this: Having a 4" RP Backflow at the base
> of riser and then tapping an antifreeze system off of the wet system but
> instead of an expansion chamber (as required by code for a double check)
> running the old style a/f 5ft loop off of this. Reasoning is since an RP
> type backflow ports when overpressurized on system side the a/f system
> can still expand through the loop like in the good ol' days.
> 
> It seems NFPA#13 only requires the expansion chamber since it would be
> impossible for the antifreeze to otherwise expand since everything is
> 'locked' in place by the double check. However with an RP backflow it
> would allow the backwards movement of water neccessary for expansion and
> the loop would perform it's duties of acting as a container for the
> antifreeze and not be ported out with the water.
> 
>   We had this arrangement ok'd by an AHJ in the past but want to see if
> there is something we're overlooking.
> 
>   thx,
> 
> 
> 
> 
> ---------------------------------
> Looking for last minute shopping deals?  Find them fast with Yahoo!
> Search.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to