Reading the annex also clarifies this point.  Thanks for the correction.

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David M.
Canham
Sent: Friday, February 29, 2008 10:57 PM
To: [email protected]
Subject: RE: Sammy express hangers

I beg to differ I see the standard as clear in that that the structure
must
be capable of holding the filled pipe plus 250 pounds.  The hanger
section
has the additional requirement of the 5 times the filled weight of the
pipe.
They are separate requirements in separate sections. 9.2.1.3.1  is in
the
section called building structure and it seems clear that the section is
refffering to the structure at the point of hanging. 

9.2.1.3* Building Structure.
9.2.1.3.1  Sprinkler piping shall be substantially supported from the
building structure, which must support the added load of the
water-filled
pipe plus a minimum of 250 lb (114 kg) applied at the point of hanging.

9.1.1.2  Hangers certified by a registered professional engineer to
include
all of the following shall be an acceptable alternative to the
requirements
of Section  9.1: 
(1)     Hangers shall be designed to support five times the weight of
the
water-filled pipe plus 250 lb (114 kg) at each point of piping support.
(2)     These points of support shall be adequate to support the system.
(3)     The spacing between hangers shall not exceed the value given for
the
type of pipe as indicated in  Table 9.2.2.1.
(4)     Hanger components shall be ferrous.
(5)     Detailed calculations shall be submitted, when required by the
reviewing authority, showing stresses developed in hangers, piping, and
fittings and safety factors allowed.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Denhardt
Sent: Friday, February 29, 2008 1:21 PM
To: [email protected]
Subject: RE: Sammy express hangers

Dave - I think you are reading too much into the standard.  The hangar
assembly must meet that requirement.  The structure only has to support
the actual weight.  You do not need to design the building's structure
to five times the weight of the water-filled piping plus 250 pounds.

Hope this helps,
John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David M.
Canham
Sent: Friday, February 29, 2008 12:21 PM
To: [email protected]
Subject: RE: Sammy express hangers

Unless the roof or Z-purlin can handle 250 punds plus the pipe the code
has
not been meet.
9.2.1.3.1  Sprinkler piping shall be substantially supported from the
building structure, which must support the added load of the
water-filled
pipe plus a minimum of 250 lb (114 kg) applied at the point of hanging.

Dave Canham
Fire Systems Solutions

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, February 29, 2008 11:26 AM
To: [email protected]
Subject: RE: Sammy express hangers

Dewayne,

The last project, which I think was similar to your situation, we used 
Sammy side-winders on the Z-purlins.  It was an ESFR project and I think

we roughly calculated the load would be about 1.1 lbs/ft2 on average.
We 
did have to check with structural to make sure the point loads could be 
handle for the cross main.  I think they told me that 2-3 lbs is added
for 
miscellaneous loads such as sprinklers, lights, HVAC.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





"Steve Leyton" <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
02/29/2008 10:39 AM
Please respond to sprinklerforum

To
<[email protected]>
cc

Subject
RE: Sammy express hangers







There's no one answer Dewayne.   Some roof decks can bear the load, some
can't.    That question should be referred to the project structural
engineer of record.  If the roof has structural concrete on it, which
many do, it can often bear the load of branch piping and arm-overs.
Some are so lightweight, they can't bear even the arm-overs.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, February 29, 2008 7:09 AM
To: [email protected]
Subject: Sammy express hangers

Has anyone run into problems with building inspectors when trying to use
the Sammy express hanger in the roof deck.  I have one telling me that
"the metal decking is designed for the roofing materials and designed
loads (rain, snow, etc.). That the design did not include other loads."
Is this true? 
Thanks,
Dewayne 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to