I may be missing something here. I see only one interpretation of the
referenced codes. For standpipe of buidlings 70 feet and higher, the water
supply has to be automatic. In other words, the NFPA 14 requirements need to
be automatically satisfied by the water supply it is connected to. If the
building is under 70 feet high, then the supply can be manual, such as
through fire department equipment. Maybe if you can state the different
possible interpretations?

In my area the buidfing code does not have this provision. It is a little
bit different. It states (in my words), if building is not fully
sprinklered, the water supply has to be automatic. If the building is
sprinklered throughout, and sprinkler system does not require a fire pump,
and standpipe has 2 1/2" hose connections, the fire dept. may provide the
required water supply (if their equipment has sufficient capacity). If the
sprinkler system needs a fire pump, then the water supply has to be
automatic.

Another section states that if the building is less than 70 feet high, then
the hose connections may be "PERMITTED TO BE" 1 1/2" instead of 2 1/2". Yet
another section states if 1 1/2" hose connections are provided, then the
water supply may be 50 psi instead of 100 psi required by NFPA 14. So what I
see mostly is contractors installing 2 1/2" hose connections with 1 1/2"
reducers, even in walk-ups so they don't have to provide the minimum 50 psi.

The different codes I have seen, have a common theme. Just adaptations for
different jurisdictions. However in the process, they are entirely messed
up, leaving the codes open for interpretations. NFPA 14 specifically has
three classes of standpipe systems. However the building codes I have seen
don't make any reference to these. It seems buildings over 70 feet are class
1. 70 feet and under are class 2 or 3 if the building is not sprinklered. So
all sprinklered buildings are class 1? If a building is sprinklered, 1 1/2"
hose is not required if 2 1/2" hose connections with 1 1/2" reducers are
provided. Are there any building codes that specifically use the terms class
1, 2 & 3 and define their application?

Tony         

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: March 1, 2008 7:33 AM
To: [email protected]
Subject: Re: Dumb Question maybe

Tom,

The Mass Code is confusing on this issue. Section 914.1 states that when
standpipes are required to be installed, they shall be automatic wet type.
This would mean that they would need to meet the flow and pressure demands
with the on site supply. However, section 914.3 Exception states that the
residual pressures are not required to met if the building is under 70 feet
high, effectively making it a manual wet standpipe. I think an
interpretation may be in order.

Todd



At 07:01 PM 2/29/2008, you wrote:
>I just did a standpipe test today.
>Mixed-use building, mid-rise, mercantile on the ground floor, 
>residential above 2-5.  56' sidewalk to parapet.
>It has a fire pump but the pump is only sized for the sprinklers (400 GPM).
>It has 2 6" combination standpipes 1-5, fully sprinklered (yup, to 13).
>We had to get a pumper truck for the standpipe test, 2 standpipes to flow.
>I had wtf when I went there 2 weeks ago to look around, they 
>(contractor) said "not our design, we just installed it", and "Plans were
approved".
>
>Is there a statute I'm unaware of that says in an installation like 
>this you have the option to size the fire pump to meet the sprinkler 
>demand and not the hose demand?  Nothing I know of in our local 
>Building Code or Ordinances.
>
>Scratching my head and getting splinters.
>
>Tom Duross
>Go Red Sox
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to