Tom, You asked about State Statues that deal with this type of arrangement. One of them is in Florida.
We have a state statue that allows for the installation of a manual wet standpipe system in buildings less than 75 feet in height. See the last sentence in the paragraph below. 553.895 (Fire Safety) (2) Except for single-family and two-family dwellings, any building which is of three stories or more and for which the construction contract is let after January 1, 1994, regardless of occupancy classification and including any building which is subject to s. 509.215, shall be equipped with an automatic sprinkler system installed in compliance with the provisions of chapter 633 and the rules and codes adopted pursuant thereto. A stand-alone parking garage constructed with noncombustible materials, the design of which is such that all levels of the garage are uniformly open to the atmosphere on all sides with percentages of openings as prescribed in the applicable building code, and which parking garage is separated from other structures by at least 20 feet, is exempt from the requirements of this subsection. Telecommunications spaces located within telecommunications buildings, if the spaces are equipped to meet an equivalent fire prevention standard approved by both the Florida Building Commission and the State Fire Marshal, are exempt from the requirements of this subsection. In a building less than 75 feet in height which is protected throughout with an approved and maintained fire sprinkler system, a manual wet standpipe, as defined in the National Fire Protection Association Standard 14, Standard for the Installation of Standpipe, Private Hydrant, and Hose Systems, shall be allowed. In Florida, this would allow someone to strictly size the pump to meet the sprinkler demand, not the standpipe demand. The standpipe demand would be provided by the fire department pumper when needed for fire department use. Nathan Hatcher -- Tel: (813) 659-2700 Fax: (813) 659-2727 [EMAIL PROTECTED] -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Friday, February 29, 2008 7:02 PM To: [email protected] Subject: Dumb Question maybe I just did a standpipe test today. Mixed-use building, mid-rise, mercantile on the ground floor, residential above 2-5. 56' sidewalk to parapet. It has a fire pump but the pump is only sized for the sprinklers (400 GPM). It has 2 6" combination standpipes 1-5, fully sprinklered (yup, to 13). We had to get a pumper truck for the standpipe test, 2 standpipes to flow. I had wtf when I went there 2 weeks ago to look around, they (contractor) said "not our design, we just installed it", and "Plans were approved". Is there a statute I'm unaware of that says in an installation like this you have the option to size the fire pump to meet the sprinkler demand and not the hose demand? Nothing I know of in our local Building Code or Ordinances. Scratching my head and getting splinters. Tom Duross Go Red Sox _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)