When I started in 1971, I think that we were only doing stagger spacing for 
extra hazard but if you have a 1961 NFPA 13 that is a treasure and there are 
not many left around.
Mike Brown

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of David Autry
Sent: Wednesday, March 12, 2008 4:00 PM
To: [email protected]
Subject: RE: Pipe scheduled systems - head stagger

Because that's they way the code reads.
My 1961 Edition
Light hazard need not be staggered, except under open wood joist. All others
shall be staggered.


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown
(TECH- GVL)
Sent: Wednesday, March 12, 2008 2:50 PM
To: [email protected]
Subject: RE: Pipe scheduled systems - head stagger

In years past staggered spacing was required in extra hazard applications.
At that time you only had 1/2 (5.6K) and 3/4" (8.0K) sprinklers. You may
also find some 3/4" pipe used on old pipe schedule systems.
Mike Brown

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, March 12, 2008 3:25 PM
To: [email protected]
Subject: Pipe scheduled systems - head stagger

I have a retrofit of a system put in in 1963 where the heads on the
branch lines are staggered.  What was the reasoning for this back then?
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to