Had someone that was adamant that they were going to protect the
valve riser with heat tape. Despite being a bad idea with little
chance of success, I couldn't say - You gotta have a valve room
although I THOUGHT it was an explicit requirement. Implicit doesn't
carry the day. Ughhhhhhhh.
Roland
On Mar 13, 2008, at 10:26 AM, <[EMAIL PROTECTED]>
<[EMAIL PROTECTED]> wrote:
Doesn't specifically say you HAVE to have one but in order to provide
heat for a dry valve in an open space it's the only choice. NFPA 13,
2007, 7.2.5.2
Craig L. Prahl, CET