Good Monday morning (at least out west) to all. I have a question I'd like to pose. It is both practical and somewhat hypothetical. This sort of relates to a question from the other day, and I didn't really catch the general consensus of the group. Anyway, on to the predicament. In an attic space, or open wood truss space, with a pitch of 4 in 12 or greater, 8.6.4.1.4.3, dictates a minimum of six feet from the eave, measured along the slope. What do you do when you have a hip at one end of the building? For example, I have a project where to maintain the six feet from the eave, I must be 5'-8.25" from the eave, measured horizontally. This distance leaves me 8'-5" from the corner of the building before crossing the hip, and being under a different slope. What about this uncovered area? Do you violate the rule with one sprinkler and pitch it to cover both areas? Do you violate the rule with two heads and install a baffle? Does NFPA have any recommendations? Do the experienced designers have any recommendations? Hopefully I explained this all well enough for everyone to understand. I would be more than happy to send a .pdf to anyone interested in contacting me off-line.
Thanks, Jimmy Waite Burtell Fire Protection, Inc. [EMAIL PROTECTED] (406) 652-7697 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)