The jurisdiction for NFPA 20 ends at the last control valve they call
for at the discharge side and NFPA 13 / 14 etc rule from that point
on. So no PRV before that valve but afterwards is AOK.
Roland
On Mar 28, 2008, at 11:16 AM, [EMAIL PROTECTED] wrote:
Forum,
Is a Pressure Reducing valve, such as the Tyco PRV-1, allowed to be
installed on the main sprinkler/standpipe header downstream of an
electric
fire pump. I know pressure relief valve is only permitted on
diesel fire
pumps. I have an estimated flow of 1,000GPM @ 165 psi. I want to
limit
the majority of system to 175 psi and I don't want to overload the
system
during churn conditions. NFPA 13 and 14 seem to allow this but
NFPA 20
says, "No pressure-regulating devices shall be installed in the
discharge
pipe except as permitted in this standard."
John Kaminski
Burt Hill
724-431-1388
http://www.burthill.com