Pipe the jockey discharge to the low side of the pressure regulating valve or the pump will cycle. I think UL still lists these at 165 so there's your system setting/jockey stop pressure. Don't forget a good safety relief downstream (like the Cla-Val 55L).
Tom The jurisdiction for NFPA 20 ends at the last control valve they call for at the discharge side and NFPA 13 / 14 etc rule from that point on. So no PRV before that valve but afterwards is AOK. Roland _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)