Pipe the jockey discharge to the low side of the pressure regulating valve
or the pump will cycle.
I think UL still lists these at 165 so there's your system setting/jockey
stop pressure.
Don't forget a good safety relief downstream (like the Cla-Val 55L).

Tom

The jurisdiction for NFPA 20 ends at the last control valve they call
for at the discharge side and NFPA 13 / 14 etc rule from that point
on. So no PRV before that valve but afterwards is AOK.

Roland