Hmmm. Notwithstanding my earlier comments, have you considered telling your client that you consulted with the Easter Bunny last weekend, who assured you that the 20 FPS downstream limit only applies to pump systems that take suction directly from Willy Wonka's Chocolate River?
Steve Leyton A. Gloop Engineering Feeling it on a Friday -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Friday, March 28, 2008 3:16 PM To: [email protected] Subject: RE: Pressure Reducing Valve An excellent answer but perhaps not stated this directly in NFPA 20?? On a current job a client (attempting to introduce a velocity limit) has stated that the velocity in a sprinkler system is limited because the system is on the discharge side of the fire pump and therefore the 20 fps applies since the sprinkler system is downstream of the pump. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell -------- Original Message -------- Subject: Re: Pressure Reducing Valve From: Roland Huggins <[EMAIL PROTECTED]> Date: Fri, March 28, 2008 2:37 pm To: [email protected] The jurisdiction for NFPA 20 ends at the last control valve they call for at the discharge side and NFPA 13 / 14 etc rule from that point on. So no PRV before that valve but afterwards is AOK. Roland On Mar 28, 2008, at 11:16 AM, [EMAIL PROTECTED] wrote: > Forum, > > Is a Pressure Reducing valve, such as the Tyco PRV-1, allowed to be > installed on the main sprinkler/standpipe header downstream of an > electric > fire pump. I know pressure relief valve is only permitted on > diesel fire > pumps. I have an estimated flow of 1,000GPM @ 165 psi. I want to > limit > the majority of system to 175 psi and I don't want to overload the > system > during churn conditions. NFPA 13 and 14 seem to allow this but > NFPA 20 > says, "No pressure-regulating devices shall be installed in the > discharge > pipe except as permitted in this standard." > > John Kaminski > Burt Hill > 724-431-1388 > http://www.burthill.com > > > This email is intended for named recipients only. > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)