As long as the area of the small room in question divided by the number
of sprinklers in the room averages less than 225 square ft per
sprinkler, the 9ft rule supercedes the S x L area calculation.
It is my understanding this allowance applies whether there is one
sprinkler or more in the small room since a small room, by definition,
can be up to 800 sq.ft. in area, thereby requiring more than one
sprinkler to protect it.

However, the 9ft allowance from a wall for a sprinkler or row of
sprinklers can only be applied off of ONE wall in the small room.
The reasoning is to allow for greater spacing in this one particular
instance to account for lights, hvac, or other ceiling obstructions in
an area than would otherwise be properly protected by the S x L spacing
requirements and is only allowed in areas of light-hazard
claassification. This is an allowance from the NFPA committee to keep
the costs of installation automatic sprinklers at a reasonable level
(without jeopardizing life safety) in these lower-hazard areas.

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
www.warp-drive.com





-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Wednesday, April 02, 2008 11:03 AM
To: [email protected]
Subject: Small Room Rule

Forum,
I trip myself every time I come across the "Small Room Rule",
A.8.6.3.2.4(c) 07' edition. Isn't the head that is 9'-0" off the wall
"covering" 270 sq.ft.?
 

Regards,

 
<http://www.firstdefensefire.com/>  

 

 




E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09530 http://www.pctools.com/spyware-doctor/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to