Ray, 

Why does the sprinkler need to be farther than 7'-6" from a wall to apply
8.6.2.1.2?  I interpret it that as long as the room meets the definition of
'small room', the area of coverage and min flow (in your example) will be
156 sf and 15.6 gpm.  Maybe the wording was somewhat different in previous
editions of 13.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
> Sent: Wednesday, April 02, 2008 11:03 AM
> To: [email protected]
> Subject: Re: Small Room Rule
> 
> Ed,
> 
> I respectfully disagree.  In a 13' x 12' (156 sqft) room protected by a
> single sprinkler, with the East-West spacing to the walls at 7-'6" and
> 5'-6, respectively, and the North-South spacing at 7'-6" x 4'-6"
> respectively, the area of coverage for the sprinkler is indeed 225
> square feet, by use of the SxL=A method from NFPA-13.  The required flow
> from that sprinkler would be 22.5 gpm, based on light hazard density.
> 
> However, if either (not both) the North-South or East-West dimensions
> were shifted so that the sprinkler is spaced greater than 7'-6" off of
> one (only one) wall, the protection area of coverage for the sprinkler
> as defined in 8.6.2.1.2 becomes 156 square feet, and the demand is
> reduced down to 15.6 gpm, based on the square footage of the room
> divided by the number of sprinklers in the room, and again a light
> hazard density.
> 
> That's an old sprinkler designers tool, taught to me by an old sprinkler
> designer tool, which was the kindest of names I eventually came to call
> him.
> PARSLEY CONSULTING
> Ken Wagoner, SET
> 760.745.6181 voice
> 760.745.0537 fax
> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> 
> 
> 
> Ed Kramer wrote:
> > Brain,
> >
> > In 'small rooms', section 8.6.2.1.2 applies.  Area of coverage is 225
> sf.
> >
> > Ed Kramer
> > Littleton, CO
> >
> >
> >
> >
> >> Forum,
> >> I trip myself every time I come across the "Small Room Rule",
> >> A.8.6.3.2.4(c) 07' edition. Isn't the head that is 9'-0" off the wall
> >> "covering" 270 sq.ft.?
> >>
> >>
> >> Regards,
> >>
> >>
> >> <http://www.firstdefensefire.com/>
> >>
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to