Ed,
I respectfully disagree. In a 13' x 12' (156 sqft) room protected by a
single sprinkler, with the East-West spacing to the walls at 7-'6" and
5'-6, respectively, and the North-South spacing at 7'-6" x 4'-6"
respectively, the area of coverage for the sprinkler is indeed 225
square feet, by use of the SxL=A method from NFPA-13. The required flow
from that sprinkler would be 22.5 gpm, based on light hazard density.
However, if either (not both) the North-South or East-West dimensions
were shifted so that the sprinkler is spaced greater than 7'-6" off of
one (only one) wall, the protection area of coverage for the sprinkler
as defined in 8.6.2.1.2 becomes 156 square feet, and the demand is
reduced down to 15.6 gpm, based on the square footage of the room
divided by the number of sprinklers in the room, and again a light
hazard density.
That's an old sprinkler designers tool, taught to me by an old sprinkler
designer tool, which was the kindest of names I eventually came to call him.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
Ed Kramer wrote:
Brain,
In 'small rooms', section 8.6.2.1.2 applies. Area of coverage is 225 sf.
Ed Kramer
Littleton, CO
Forum,
I trip myself every time I come across the "Small Room Rule",
A.8.6.3.2.4(c) 07' edition. Isn't the head that is 9'-0" off the wall
"covering" 270 sq.ft.?
Regards,
<http://www.firstdefensefire.com/>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)