Sorry Ron G., I'm not harping on your little mistake...I posted this a
half an hour ago before anyone else replied.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reed
Roisum
Sent: Tuesday, April 08, 2008 11:41 AM
To: [email protected]
Subject: RE: Failed Bucket Test

I believe Ron's math is correct.  57.7' of elevation x .433 psi/ft = 25
psi

Reed A. Roisum
Fire Protection Technician
NICET Level III
 
Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079
 
Direct Number: 701.280.8580
Mobile: 701.212.8810
Main Office: 701.280.8500

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Tuesday, April 08, 2008 11:13 AM
To: [email protected]
Subject: Re: Failed Bucket Test

Ron,

Check your math: 25.0 x 0.433 = 10.825

On Apr 8, 2008, at 8:47 AM, Fletcher, Ron wrote:

> 25 psi equals 57.7 feet of elevation and partially closed valves can
> account for a reduced static pressure when dealing with city water
> mains.
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ron
> Greenman
> Sent: Tuesday, April 08, 2008 8:32 AM
> To: [email protected]
> Subject: Re: Failed Bucket Test
>
> Brian,
>
> Static doesn't change, even with a blockage (recovery time is slower  
> but
> eventually reaches the pre-recorded pressure--hence the value of a  
> main
> drain test), unless the original test was done during off-peak and  
> your
> bucket test was done during peak, there is a pump involved that is not
> coming on or has been removed from service (your bucket test may not
> have enough demand to fire it up but a hydrant test would--this begs  
> the
> differences in static), the grid has been changed and the source, if
> gravity, is lower, relative to the site, than before, the level of the
> tank was lower during your test (25 psi equals a little less than 11
> feet) or the guy that produced the original numbers didn't know what  
> he
> was doing (I got a report once that showed the residual pressure and
> velocity pressure to be the same--the water guy wouldn't budge). If
> you're in a residential area I'd look at the time of day and time of
> year the test was done as well as the area, read grid, growth since  
> the
> time the test was done. Mid day and mid night are off peak times as is
> winter in general during peak. The tanks may be low and your test may
> have been done during or at the end of morning peak or the beginning  
> of
> evening peak. The original test may have been done during summer at
> midnight when usage was down and the tanks freshly replenished for
> tomorrow's lawn watering. Lots of possibilities. I think our reliable,
> automatic water supplies are less than reliable but the alternative
> seems to be stored water and pumps--extra equipment to fail.
>
> On Tue, Apr 8, 2008 at 7:22 AM, Brian Harris
> <[EMAIL PROTECTED]> wrote:
>>
>
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

Ron Greenman
...at home





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum