I am sure if you contact the Cobb County Georgia Fire Department they will tell 
you about a lot of failures particularly when they first started.  The local 
contractors know about the test and check it themselves before they call for an 
inspection.  You guys are very diligent about your calculations etc. but there 
is a big world of contractors and engineers that are not part of this group who 
are not as versed in design as you may be.  It is a very simple test and it 
empirically proves that the system design is correct.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jamie Seidl
Sent: Wednesday, April 09, 2008 3:17 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

I've only had one that failed.  It turned out that the plumber had installed a 
1" line into the building from the meter (2" thru the slab) when we needed a 2" 
line from the meter.  That is the reason for the bucket test, make sure the 
calc's work.  We could all argue quite correctly that it's not necessary but I 
am very comfortable with doing these test.  It just verifies that the whole 
system (at least the remote area) was installed correctly and will perform as 
intended.

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Wednesday, April 09, 2008 3:12 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

Now that we have some what and where how about the why?

Brian's problem would have been discovered by looking at the gauge or main
drain, a bucket test wasn't really necessary.  Is there some problem with
hydraulic calcs?  How many actually fail?

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [EMAIL PROTECTED]

Mail: P.O. Box 69
        Waverly, MN 55390

Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jamie Seidl
Sent: Wednesday, April 09, 2008 1:23 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

Quite a few in the North Carolina and Georgia area.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Wednesday, April 09, 2008 2:20 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

This is the first time I've heard it being done for 13R. 13D, yes. But not
13R. Are there other jurisdictions requiring a bucket test for 13R?

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: April 9, 2008 12:01 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: What is a Bucket Test?

A bucket test / barrel test is when you remove a head(s) in the remote area
and fill up a bucket/barrel to see if it is flowing the gpm the is called
for in the calc's. In our case with the density and heads we are using that
would be 20 gpm, we are getting around 15 gpm.


Brian Harris
FDFP INC.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, April 09, 2008 1:50 PM
To: sprinklerforum@firesprinkler.org
Subject: What is a Bucket Test?

Perhaps a dumb question, but what is a bucket test and is it conducted the
same way in every jurisdiction?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: Failed Bucket Test
From: "Brian Harris" <[EMAIL PROTECTED]>
Date: Mon, April 07, 2008 2:30 pm
To: <sprinklerforum@firesprinkler.org>

Fellow forum people:
I have a situation where we have designed and installed a 13R system, it is
completely finished and wham-o we fail the bucket test! Our system was
designed based on the flow test provided by the city fire dept., turns out
that a test taken now with the failed test shows a 25% drop in static &
residual pressures, hence the failed test. Of course the owner is looking to
us to pull a magic rabbit out of our #$% , err I mean hat, we have tried a
few different things but with that big of a pressure loss there's really not
much we can do. I don't feel it's our liability at this point since we went
off the city's water flow test and per the calc's we were good, any
thoughts?


Regards,


<http://www.firstdefensefire.com/>








E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09560 http://www.pctools.com/spyware-doctor/
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)





E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09590 http://www.pctools.com/spyware-doctor/





E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
5.09590 http://www.pctools.com/spyware-doctor/
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to