Yes, asinine.

On Wed, Apr 9, 2008 at 9:04 PM, IPA <[EMAIL PROTECTED]> wrote:
> This whole bucket thing sounds asinine to me... I mean, obviously Brian has
>  a problem here with the water supply but the bucket test in general doesn't
>  sound real
>  practical. Anyone could've looked at the guage and realized their
>  was a problem without a bunch of people sitting around holding
>  buckets under open heads. Hydraulic calculations are theoretical in
>  nature...
>  This especially doesn't make much sense if ahj's are requiring this for 13d
>  systems which
>  can be calculated based upon a static pressure only....
>
>
>
>
>  On 4/9/08, A.P.Silva <[EMAIL PROTECTED]> wrote:
>  >
>  > The system is wet. You make up an assembly that will include a valve and
>  > orifice. The sprinkler head/s at the test location removed and substituted
>  > with the assembly. The valve at the outlet is opened and water collected
>  > in
>  > a bucket. In essence the test is a verification of the design calculations
>  > and installation. And I guess the water supply.
>  >
>  >
>  > Tony
>  >
>  > -----Original Message-----
>  > From: [EMAIL PROTECTED]
>  > [mailto:[EMAIL PROTECTED] On Behalf Of
>  >
>  > [EMAIL PROTECTED]
>  > Sent: April 9, 2008 5:58 PM
>  > To: [email protected]
>  > Subject: RE: What is a Bucket Test?
>  >
>  > So, you start with the system dry, then open the valve?
>  >
>  > Bill Brooks
>  >
>  > William N. Brooks, P.E.
>  > Brooks Fire Protection Engineering Inc.
>  > 372 Wilett Drive
>  > Severna Park, MD 21146
>  > 410-544-3620 Phone
>  > 410-544-3032 FAX
>  > 412-400-6528 Cell
>  >
>  > -------- Original Message --------
>  > Subject: RE: What is a Bucket Test?
>  > From: "A.P.Silva" <[EMAIL PROTECTED]>
>  > Date: Wed, April 09, 2008 6:17 pm
>  > To: [email protected]
>  >
>  > It should be same orifice as head. Also same number of heads as in design.
>  > What will a single 1/2" outlet tell you when you have 4, 7/16" outlets in
>  > your design area.
>  >
>  > At the time bucket tests were starting to be done, residential heads had
>  > two
>  > flow requirements. One for single head and another for multiple heads.
>  > So
>  > for 13D systems the bucket test was done with a single head flowing and
>  > also
>  > for two heads flowing simultaneously. An actual head with the guts broken
>  > was used at the outlet. At least this is how it is done in my area.
>  >
>  > Tony
>  >
>  > -----Original Message-----
>  > From: [EMAIL PROTECTED]
>  > [mailto:[EMAIL PROTECTED] On Behalf Of IPA
>  > Sent: April 9, 2008 1:47 PM
>  > To: [email protected]
>  > Subject: Re: What is a Bucket Test?
>  >
>  > What kind of variance in calcs from actual bucket test results are
>  > considered acceptable? I'm just curious since taking out the head and
>  > flowing straight from a 1/2" threaded outlet vs. flowing a 7/16" orifice
>  > (like a 4.2k sprinkler w/ element removed) could possibly work in your
>  > favor
>  > to a small degree but could also work against you depending on what
>  > k-factor
>  > of sprinkler you used.
>  >
>  >
>  > In a 13R bucket test do you actually remove more than one sprinkler and
>  > flow
>  > up to four? Or is it always just one? Seems like a source calc w/ one
>  > sprinkler flowing would make more sense if you're only required to bucket
>  > test one sprinkler...
>  >
>  > -B-
>  >
>  >
>  >
>  >
>  > On 4/9/08, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote:
>  > >
>  > > If you have a really bad water supply, instead of a pitot you use a
>  > > 5-gallon bucket and a stop watch. 8-)
>  > >
>  > >
>  > > At 02:19 PM 4/9/2008, you wrote:
>  > >
>  > > > This is the first time I've heard it being done for 13R. 13D, yes.
>  > > > But not 13R. Are there other jurisdictions requiring a bucket test
>  > > > for 13R?
>  > > >
>  > > > Tony
>  > > >
>  > > > -----Original Message-----
>  > > > From: [EMAIL PROTECTED]
>  > > > [mailto:[EMAIL PROTECTED] On Behalf Of Brian
>  > > > Harris
>  > > > Sent: April 9, 2008 12:01 PM
>  > > > To: [email protected]
>  > > > Subject: RE: What is a Bucket Test?
>  > > >
>  > > > A bucket test / barrel test is when you remove a head(s) in the
>  > > > remote area and fill up a bucket/barrel to see if it is flowing the
>  > > > gpm the is called for in the calc's. In our case with the density
>  > > > and heads we are using that would be 20 gpm, we are getting around
>  > > > 15 gpm.
>  > > >
>  > > >
>  > > > Brian Harris
>  > > > FDFP INC.
>  > > >
>  > > > -----Original Message-----
>  > > > From: [EMAIL PROTECTED]
>  > > > [mailto:[EMAIL PROTECTED] On Behalf Of
>  > > > [EMAIL PROTECTED]
>  > > > Sent: Wednesday, April 09, 2008 1:50 PM
>  > > > To: [email protected]
>  > > > Subject: What is a Bucket Test?
>  > > >
>  > > > Perhaps a dumb question, but what is a bucket test and is it
>  > > > conducted the same way in every jurisdiction?
>  > > >
>  > > > Bill Brooks
>  > > >
>  > > > William N. Brooks, P.E.
>  > > > Brooks Fire Protection Engineering Inc.
>  > > > 372 Wilett Drive
>  > > > Severna Park, MD 21146
>  > > > 410-544-3620 Phone
>  > > > 410-544-3032 FAX
>  > > > 412-400-6528 Cell
>  > > >
>  > > > -------- Original Message --------
>  > > > Subject: Failed Bucket Test
>  > > > From: "Brian Harris" <[EMAIL PROTECTED]>
>  > > > Date: Mon, April 07, 2008 2:30 pm
>  > > > To: <[email protected]>
>  > > >
>  > > > Fellow forum people:
>  > > > I have a situation where we have designed and installed a 13R
>  > > > system, it is completely finished and wham-o we fail the bucket
>  > > > test! Our system was designed based on the flow test provided by the
>  > > > city fire dept., turns out that a test taken now with the failed
>  > > > test shows a 25% drop in static & residual pressures, hence the
>  > > > failed test. Of course the owner is looking to us to pull a magic
>  > > > rabbit out of our #$% , err I mean hat, we have tried a few
>  > > > different things but with that big of a pressure loss there's really
>  > > > not much we can do. I don't feel it's our liability at this point
>  > > > since we went off the city's water flow test and per the calc's we
>  > > > were good, any thoughts?
>  > > >
>  > > >
>  > > > Regards,
>  > > >
>  > > >
>  > > > <http://www.firstdefensefire.com/>
>  > > >
>  > > >
>  > > >
>  > > >
>  > > >
>  > > >
>  > > >
>  > > >
>  > > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
>  > > > 5.09560 http://www.pctools.com/spyware-doctor/
>  > > > _______________________________________________
>  > > > Sprinklerforum mailing list
>  > > > [email protected]
>  > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  > > >
>  > > > To Unsubscribe, send an email
>  > > >
>  > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > <[EMAIL PROTECTED]
>  > sprinkler.org>
>  > > > (Put the word unsubscribe in the subject field)
>  > > >
>  > > > _______________________________________________
>  > > > Sprinklerforum mailing list
>  > > > [email protected]
>  > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  > > >
>  > > > To Unsubscribe, send an email
>  > > >
>  > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > <[EMAIL PROTECTED]
>  > sprinkler.org>
>  > > > (Put the word unsubscribe in the subject field)
>  > > >
>  > > >
>  > > >
>  > > >
>  > > >
>  > > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
>  > > > 5.09590 http://www.pctools.com/spyware-doctor/
>  > > >
>  > > >
>  > > >
>  > > >
>  > > >
>  > > > E-mail message checked by Spyware Doctor (5.5.0.178) Database version:
>  > > > 5.09590 http://www.pctools.com/spyware-doctor/
>  > > > _______________________________________________
>  > > > Sprinklerforum mailing list
>  > > > [email protected]
>  > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  > > >
>  > > > To Unsubscribe, send an email
>  > > >
>  > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > <[EMAIL PROTECTED]
>  > sprinkler.org>
>  > > > (Put the word unsubscribe in the subject field)
>  > > >
>  > > > _______________________________________________
>  > > > Sprinklerforum mailing list
>  > > > [email protected]
>  > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  > > >
>  > > > To Unsubscribe, send an email
>  > > >
>  > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > <[EMAIL PROTECTED]
>  > sprinkler.org>
>  > > > (Put the word unsubscribe in the subject field)
>  > > >
>  > >
>  > > Todd G. Williams, PE
>  > > Fire Protection Design/Consulting
>  > > Stonington, Connecticut
>  > > www.fpdc.com
>  > > 860.535.2080 _______________________________________________
>  > > Sprinklerforum mailing list
>  > > [email protected]
>  > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  > >
>  > > To Unsubscribe, send an email
>  > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > <[EMAIL PROTECTED]
>  > sprinkler.org>
>  > > (Put the word unsubscribe in the subject field)
>  > >
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > [email protected]
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  >
>  > To Unsubscribe, send an email
>  > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > (Put the word unsubscribe in the subject field)
>  >
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > [email protected]
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  >
>  > To Unsubscribe, send an email
>  > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > (Put the word unsubscribe in the subject field)
>  >
>  >
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > [email protected]
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  >
>  > To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > (Put the word unsubscribe in the subject field)
>  >
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > [email protected]
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  >
>  > To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>  > (Put the word unsubscribe in the subject field)
>  >
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....