Todd & Ron, Thanks for your input. I was planning on just using a butterfly valve at each floor but forgot about the drains. I don't think I'll check the floors off. Each floor is only about 2,500 Sq Ft.
Thanks again. Randy -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Wednesday, April 09, 2008 5:44 PM To: [email protected] Subject: Re: Dry standpipe and dry systems. Randy, Code wise, I don't anything that restricts you from doing that. I always have felt uncomfortable with the idea of a standpipe on a dry valve, but perhaps some of the fire fighters amongst us could help up on the merits of those. The problem I see with the floor control on a dry system is that most floor controls contain flow switches, which are a no-no. You could install a valve, but probably not anything to monitor flow. Also, I'm not sure how the check valve requirement would play in to this. There is a restriction on using check valves to separate a dry system, but does that prohibit check valves for any reason? It could. Todd At 06:51 PM 4/9/2008, you wrote: >Forum Members, > > > >I have a two part question. > >1. Can I have a combined standpipe on a dry system? I have 4 story factory >building that's not heated. Fourth floor is above 30 feet so I need a >standpipe. I have a heated pump room with a dry pipe valve. I was first >looking at the project with a dry manual standpipe and a separate dry >sprinkler system riser. I would like to combine the two and save piping > > > >2. Is it OK to put floor control valves in on dry pipe system? There is a >removable section of roof where they take equipment out. I would like to >give the facility the ability to shut individuals floors down for >modification to the systems. > > > >Thanks, > > > >Randy Knutson > >Shilo Automatic Sprinkler, Inc. > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)