As I remember the return bend was to help insure that creeping crud and 
corrosion does not build up on the orifice inlet of the sprinkler and cause 
problems with the operation of the sprinkler.  Or maybe I am just getting brain 
hiccups.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Thursday, May 08, 2008 9:34 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Return Bends

I know it doesn't seem right. But is it achieving its intent? Return bends
are used to prevent scale and other sediments being trapped at the head. To
some extent, at least except from the individual branchline, won't this be
achieved?

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: May 8, 2008 5:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Return Bends

what is being proposed to you is a line on a riser nipple off of the main
NOT return bends.  The return bend is there for a reason and what is being
proposed to you does not serve the purpose.  The suggestion should be
rejected.

Garth

----- Original Message -----
From: "A.P.Silva" <[EMAIL PROTECTED]>
To: <sprinklerforum@firesprinkler.org>
Sent: Wednesday, May 07, 2008 11:08 PM
Subject: Return Bends


> I have a situation, dry system running in heated space below the attic in
> part of the building. In other parts, within the attic space. Where it is
> running in the heated area, sprinklers are pendent type. So the need for
dry
> pendents or return bends. The contractor doesn't want to install
individual
> return bends for each pendent head (for cost reasons). Instead he is
> proposing to make the entire branchline as the return bend. The branchline
> to have a riser at the connection to the main. Then from the branchline
drop
> down directly to each pendent head. Any problems?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to