But I would argue it is NOT o.k. to trap water in a drop - heated or
otherwise.  We have seen examples of drops with trapped water, where at
the water/air interface, scale developed to the point of total blockage.
Which brings up the point - what do you do for the 200 psi hydro-test?
Either you drain all return bends; or test using plugs, then install
sprinklers without the 200 psi hydro.  Which is correct?  Either way,
the sprinklers are installed or re-installed without the benefit of the
200 psi hydro.

Mark A. Sornsin, PE 
Fire Protection Engineer 
Ulteig Engineers, Inc. 
Fargo, ND  
701.280.8591
[EMAIL PROTECTED] 
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Thursday, May 08, 2008 11:02 AM
To: [email protected]
Subject: RE: Return Bends

That is my understanding also. When the piping undergoes the 200 psi
pressure test, all drops (return bends or otherwise) would trap water,
which
is okay as it is in a heated area. As far as I know, no one drains the
drop
of a return bend. So I think it would be safe to say the intent of the
return bend is to minimize "creeping crud and corrosion". 

So the question is: would the riser nipple at the main also achieve
this? I
know, the junk from the individual branchline can get deposited at the
orifices. But the riser nipple will isloate the rest of the system. Any
thoughts?

Tony  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mike
Brown
(TECH- GVL)
Sent: May 8, 2008 7:51 
To: [email protected]
Subject: RE: Return Bends

As I remember the return bend was to help insure that creeping crud and
corrosion does not build up on the orifice inlet of the sprinkler and
cause
problems with the operation of the sprinkler.  Or maybe I am just
getting
brain hiccups.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent: Thursday, May 08, 2008 9:34 AM
To: [email protected]
Subject: RE: Return Bends

I know it doesn't seem right. But is it achieving its intent? Return
bends
are used to prevent scale and other sediments being trapped at the head.
To
some extent, at least except from the individual branchline, won't this
be
achieved?

Tony

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: May 8, 2008 5:07 AM
To: [email protected]
Subject: Re: Return Bends

what is being proposed to you is a line on a riser nipple off of the
main
NOT return bends.  The return bend is there for a reason and what is
being
proposed to you does not serve the purpose.  The suggestion should be
rejected.

Garth

----- Original Message -----
From: "A.P.Silva" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Wednesday, May 07, 2008 11:08 PM
Subject: Return Bends


> I have a situation, dry system running in heated space below the attic

> in part of the building. In other parts, within the attic space. Where

> it is running in the heated area, sprinklers are pendent type. So the 
> need for
dry
> pendents or return bends. The contractor doesn't want to install
individual
> return bends for each pendent head (for cost reasons). Instead he is 
> proposing to make the entire branchline as the return bend. The 
> branchline to have a riser at the connection to the main. Then from 
> the branchline
drop
> down directly to each pendent head. Any problems?
>
> Tony
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to