A question for where there is healthy pressures.  Around 
here 60 is considered high.  I know places with 28 static. 
 Got a OHII system that needs to be changed to EXII. 
 That's not negotiable.  It's a 40 yo pipe schedule 
system.  That appears to be in good shape.  The BL need to 
be replaced for 100 sq.ft.  but the main even the last 12' 
of 2.5", 25' of 3" and 36' of 3.5" can fly without being 
replaced.  The openings are where I need them.  There is a 
FP with about 140 psi at the 900gpm demand.  The "problem" 
is the velocities in one segment of pipe are just about 40 
(last piece of 3") and about 30 in the 3.5".  I quote 
problem because I know 13 has no limit, this is not FM. 
 There is still better than 15 psi safety.

So the question is where you have pressure do you 
typically burn it up with small pipe size at the cost of 
velocities getting high or do you leave a lot of safety? 
 Again not FM and OK per 13.

Any thoughts on why this is a bad idea?  It's easy to say 
just pull the offending pipe.  In reality though you all 
know the competitive market and spending owners money.