This always gets me going. I love when AHJ's put in an arbitrary maximum
velocity without any logical backup, other than they read that it's better
to keep them low. (Usually in some plumbing magazine where noise is an
issue.) While we all usually do a demand calc, with a nice safety margin,
like 15Psi for a 140Psi supply, so let's say that we are limited by the AHJ
to 30 FPS. Our calc's all work out and we're off. But what actually happens
in a fire? Does the fire say "I only want this much water, and no more!"? Of
course not everyone knows it takes everything the sprinkler system will
give. If the fire is small, all the affected heads overflow because they
have a higher residual pressure, than was calc'ed. If the fire is the exact
size of the design area, the heads still over flow the design because of the
"safety factor" that extra 15Psi. and if the fire overwhelms the system
design, well again we overflow the system but not necessarily individual
heads. So which scenario created higher velocities than were designed. ALL
OF THEM!!! 

I always love to give the AHJ a supply calc. (After they return my approved
submittal) and show them what really happens if those same heads and area
are now flowing, and if I have time I like to do one for some other area as
well.

If you've got the Psi use it. If there is no limit why not use what works? 


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Monday, June 02, 2008 8:47 AM
To: [email protected]
Subject: High velocities



A question for where there is healthy pressures.  Around here 60 is
considered high.  I know places with 28 static. 
 Got a OHII system that needs to be changed to EXII. 
 That's not negotiable.  It's a 40 yo pipe schedule system.  That appears to
be in good shape.  The BL need to be replaced for 100 sq.ft.  but the main
even the last 12' 
of 2.5", 25' of 3" and 36' of 3.5" can fly without being replaced.  The
openings are where I need them.  There is a FP with about 140 psi at the
900gpm demand.  The "problem" 
is the velocities in one segment of pipe are just about 40 (last piece of
3") and about 30 in the 3.5".  I quote problem because I know 13 has no
limit, this is not FM. 
 There is still better than 15 psi safety.

So the question is where you have pressure do you typically burn it up with
small pipe size at the cost of velocities getting high or do you leave a lot
of safety? 
 Again not FM and OK per 13.

Any thoughts on why this is a bad idea?  It's easy to say just pull the
offending pipe.  In reality though you all know the competitive market and
spending owners money.


Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to