If you exceed the 2/12 (Flat) ceiling anywhere, increase by 30% Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Tuesday, June 03, 2008 10:24 AM To: AFSA Subject: Barrel Ceiling I'm looking at a project which has a room about 40 feet wide and has a ceiling which is barrel shaped. It is not a deep barrel but rather a large radius, it starts out at the wall with about a 3/12 pitch and as it nears the apex it, of course, levels out. In trying to apply the rule for design area increase due to sloping ceilings this situation seems not to fit the written text very clearly. Can anyone offer an opinion or point me towards a standard/code I can apply? Thanks, Russell _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)