I would agree, but only if you could have a head located far enough from the
edge of the vault so it was on a slope less than or = to 2/12 then the heads
around the perimeter of the vault would act similar to a "Ceiling Pocket"
with heads in the pocket. (In the barrel) But because this starts at a wall,
it is no ceiling pocket. And I just don't think that you can get far enough
in to have the heads on a slope of less than 2/12. The only way to check
this is to know the true shape of the ceiling. Is it part of a true ARC or
some other curved shape? What is the highest point, maybe you can still get
a reduction in area to offset some of the 30% by using QR.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Tuesday, June 03, 2008 3:49 PM
To: [email protected]
Subject: Re: Barrel Ceiling

Thom,

I'm not so sure I agree. if you plot out the degrees between where 3
1/2//12 and 0//12 on a quarter circle you get a pretty shallow arc.
The 3 1/2//12 to 2 1/2//12 portion is a lot like attaching a collar tie to a
45 degree rafter a foot or so above the plate, rocking it all and then
arguing for a 30% increase based on the foot or so section around the edge
that's at 6//12. Since code does not address a solution to either situation
the simple, conservative approach would be yours but I think an average
slope along the entire arc should be the criterion. I didn't calculate this
but I'd bet it's less than 2//12.

On Tue, Jun 3, 2008 at 1:34 PM, Thom McMahon <[EMAIL PROTECTED]>
wrote:
> If you exceed the 2/12 (Flat) ceiling anywhere, increase by 30%
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Russell
> Sent: Tuesday, June 03, 2008 10:24 AM
> To: AFSA
> Subject: Barrel Ceiling
>
> I'm looking at a project which has a room about 40 feet wide and has a 
> ceiling which is barrel shaped. It is not a deep barrel but rather a 
> large radius, it starts out at the wall with about a 3/12 pitch and as 
> it nears the apex it, of course, levels out. In trying to apply the 
> rule for design area increase due to sloping ceilings this situation 
> seems not to fit the written text very clearly. Can anyone offer an 
> opinion or point me towards a standard/code I can apply?
>
>
>
> Thanks,
>
> Russell
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email 
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to