Subject: calcs with pipe replacement


> I walked through an attic this afternoon where all of the existing 
> mains need to be replaced. The piping is 3" schedule 10 black steel, 
> that is developing leaks after 17 years (we found another one on our 
> tour). The proposal is out there to replace the existing with 3" 
> schedule 40 galvanized (and provide proper pitch). I did a couple of 
> quick calculations and at 250 gpm, the friction loss per foot for the 
> two pipes is very close to the same. (.077 for the sch 10 black v. 
> .075 for the sch 40 galv). My guess is that the difference in 
> pressure would be about 0.75 psi. The calc has about 12 psi 
> remaining. If this was strictly a pipe replacement (no other 
> modifications), would you recommend new hydraulic calculations?
> 
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080  