Todd, based on the fact that this is a repair, as mentioned, AND the fact
that you're replacing pipe that *should* have been calculated with a
hazen-williams c-factor of 100 (black steel) with piping that has a c-factor
of 120 (galvanized) - I would say you're probably going to be alright - but
better safe than sorry - so why not run calcs?

-B-



On 6/5/08, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote:
>
> To do this job correctly (operative word) will require a lot more than just
> pipe replacement and thus will need to be recalculated. As an example, to
> properly pitch the pipe will require replacement of most of the dry pendents
> feeding the floor below. The additional 30% increase and a few other things
> have already been mentioned to the contractor. However, the job spec treats
> this as a repair and doesn't really try to solve the problem of water
> trapped in mains (except they want an add for an air dryer in the quote)
>
> My question was more academic in that if you replace one pipe with a
> different type of pipe with a similar loss per foot and make no other
> changes, would it necessarily have to be recalculated. When does repair
> become modification?
>
>
>
> At 12:31 AM 6/5/2008, you wrote:
>
>> If I had high confidence of all the following, I wouldn't see the need for
>> new calcs:
>>        -  Strictly pipe replacement (no added offsets, elbows, riser
>> nipples, etc)
>>        -  The original calcs were accurate (done properly and reflect 'as
>> built' conditions)
>>        -  Water supply hasn't deteriorated.
>>
>> A bit of a side note - if the attic has a roof with slope greater than
>> 2/12,
>> the design area very likely didn't include a 30% increase for the slope.
>> That requirement didn't appear in 13 until 1996.  But since the pipe
>> replacement is legitimately a repair, you probably don't need to meet any
>> standard other than what was in effect 17 years ago.
>>
>> Ed Kramer
>> Littleton, CO
>>
>>
>> > I walked through an attic this afternoon where all of the existing
>> > mains need to be replaced. The piping is 3" schedule 10 black steel,
>> > that is developing leaks after 17 years (we found another one on our
>> > tour). The proposal is out there to replace the existing with 3"
>> > schedule 40 galvanized (and provide proper pitch). I did a couple of
>> > quick calculations and at 250 gpm, the friction loss per foot for the
>> > two pipes is very close to the same. (.077 for the sch 10 black v.
>> > .075 for the sch 40 galv). My guess is that the difference in
>> > pressure would be about 0.75 psi. The calc has about 12 psi
>> > remaining. If this was strictly a pipe replacement (no other
>> > modifications), would you recommend new hydraulic calculations?
>> >
>> > Todd G. Williams, PE
>> > Fire Protection Design/Consulting
>> > Stonington, Connecticut
>> > www.fpdc.com
>> > 860.535.2080
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
>> (Put the word unsubscribe in the subject field)
>>
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to